I was sent to do a EICR on a DB in a commercial kitchen and could do with some opinions on which codes to give. seeing as I haven't done a EICR since the spring and only doing new installation certs I have a fair idea but feel a bit out of confidence with it.
thanks in advance for your input:
1 - cables from the DB not in CMS or sufficiently supported
2 - outer sheath on T&E cables stripped back outside of DB
3 - no blank covers on DB
4 - no busbar cover
5 - no rcd protection on socket outlets
6 - 4 cables terminated into one of the MCBs
7 - different ill fitting MCBs in DB
8 - 20mm holes in DB
thats all i can think of off the top of my head, im sure theres more if i'm back there tomorrow il upload a picture it looks rough!
i'd say
1 - c3
2 - c2
3 - c1
4 - c2
5 - c2
6 - c3/FI
7 - c3
8 - c2
??