Had my 1552 for over 4 years. It has displayed that symbol maybe 3 times.
It did not go ---- up immediately after.
It would be nice if a megger chap gave a thorough detailed explanation of what this symbol means?
The noise warning symbol is a sine-wave with a spike on the positive half cycle, seen at the top of the display just right of centre on an Megger MFT 15xx.
The noise warning symbol on a Megger MFT 15xx, 17xx or 18xx is very rare event, due to the multi-pulse, noise cancellation measurement method employed. It is because of this patented technique that the Megger MFTs gets unfair criticism from users of other MFTs (Fluke devotees in particular) for it's apparently slow "No-trip" test, however, Megger users get the last laugh because they very rarely have their test inhibited by a noise error whereas Fluke users see their equivalent, Error 5, fairly regularly even in the domestic environment. Most Megger users reckon on it occurring about once a year, maybe a few more if you do lot of industrial work, and usually on a No-Trip loop test.
The noise warning symbol is displayed when there is excessive noise on the supply. Noise or transients on the supply voltage can effect the accuracy of the loop measurement during the test and introduce an error in the reading. The noise or transient on the supply voltage are usually caused by active appliances or equipment on the supply, the source usually this internal to the installation, but equally may be caused by an external source. Internal sources can usually be isolated (switched OFF) eg. automatically switched loads and motor controllers, however, when external sources are the cause it may require testing at a different time of day to avoid the active period, during their lunch hour or after normal working hours eg. A garage down the road maybe using welding equipment or the Vets /Doctors surgery using X-ray equipment.
If the noise warning symbol is displayed the reading should be treated as in-accurate and the test repeated, usually a second test is all that is required to get a reliable reading. If the noise symbol continually appears on repeated test the cause should be investigated.
[FONT=&]In an industrial environment where continuous production must be maintained and the noise source cannot be isolated, often the only thing you can do in the short-term is to take a series of readings and record the average value to minimise the error.