On job today at small toruing caravan park entire site is TT

The toruing pitches are newly cabled in last year sometime, the office block wasnt touched, but had been refurbished by MWPS (i think) the previous year A total rats nest in the loft, with cables cut and just left floating.

The site distrubtion shed (local Earth Rod) feeds the office block as well as everyting else, into a CU, with local earth rod, upon testing, get a good 10 Ohms with cable connected to CU, testing with cable alone, no reading, the cable leaves the cu through the wall down into the concrete and under slabs and tarmac and into the earth rod pit, No continuity and the clamp on the rod is broken. [ElectriciansForums.net] Earth Rod Cable and Clamp Fault [ElectriciansForums.net] Earth Rod Cable and Clamp Fault

Am I correct in telling client that the local earth cable and rod clamp require fixing so as not to have to rely on the other earth rods around the site, or can this one be disconnected ( I am going with fixing the local rod arrangement).

On another note, the CU in the office block also feeds another CU for the boiler room via 10mm cable off 50A MCB, they just left the bare earth lying in the CU whilst running a 10mm separete earth alongside the cable.
[ElectriciansForums.net] Earth Rod Cable and Clamp Fault

How do you peeps tidy up redundant cables, for example, a few of the switches have cables running up from them into the loft space, and just left floating, I can disconnect them from the switch but cannot pull the cables up the wall and dispose of them, must be pinned to the wall or stuck somehow, how do you terminate them in the switch, do you cut them off right at the inlet or do you terminate the cables and leave cluttering up the switch space.
 
I shouldn't have to tell you, that this local earth rods cable needs to be reconnected to the earth rod, ..end of!!!

As for the bare earth cable in the CU, why not sleeve it and connect it to the earth bars at each end?? Got to be better than just leaving it as it is!!

I'll let others here convey how they would clean up the redundant cable mess above the false ceilings.... lol!!
 

Reply to Earth Rod Cable and Clamp Fault in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
888
  • Question
Could be damage to the N core touching the fabric of the building but the CPC of that cable is insulated from both. I.E. a screw clipping the edge...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top