531.2.9 what does it mean? | on ElectriciansForums
  • Thread starter brman
  • Start date
  • Replies 15
  • Views 4K

Discuss 531.2.9 what does it mean? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

B

brman

Ok, I am sad and have just been re-reading the regs on RCDs for additional protection.
This lead me to 531.2.9 which is talking about the need for descrimination on series RCDs. Ok so far.

but then it has a note; "in such cases the downstream RCD may need to disconnect all live conductors"

To me this is saying that the downstream RCD might need to switch neutral as well as line(s). ie. not be a single pole RCBO.

Is the the right interpretation and why would this be the case?
 
not sure, b ut could it be that the downstream RCD is used as an isolation device for a sub-main and as such needs to disconnect all live conductors inc. the neutral.
 
not sure, b ut could it be that the downstream RCD is used as an isolation device for a sub-main and as such needs to disconnect all live conductors inc. the neutral.

Thanks, yes, use as isolation was all I could think of but then why single out the downstream RCD specifically. Surely that could equally apply to the upstream RCD?
 
Is an rcbo not a dp switching device?

someone might correct me but I think most domestic RCBOs are single pole. I believe you can get DP ones but I don't think they are common.

I've just been reading a thread about SP RCBOs and the fact they do not break the neutral. The arguement being that this is not much good if it is a N->E fault. I suppose if the upstream RCD is DP and the downstream SP then a neutral to earth fault would trip both of them, meaning you don't have discrimination.

EDIT: thinking more I am still not sure. I am trying to think of a situation where a neutral to earth fault on a final circuit would not be fed by that specific circuits Line, meaning the downstream sp RCBO would effective clear the fault by isolating the line conductor. If the neutral for the whole system is significantly above earth then I would be happy that it needs the upstream RCD to clear it. Not sure if that makes sense.....
 
Thanks, yes, use as isolation was all I could think of but then why single out the downstream RCD specifically. Surely that could equally apply to the upstream RCD?


i think the answer to that is "local isolation"
 
If there is a neutral earth fault after the downstream SP RCD that causes it to trip disconnecting the line conductor, there is still a neutral earth connection "visible" to the upstream RCD which will still trip because the downstream RCD did not clear the fault.
Although the current will be reduced by tripping the line there will still be transient current flowing possibly from another circuit that can use the earth path.
 
If there is a neutral earth fault after the downstream SP RCD that causes it to trip disconnecting the line conductor, there is still a neutral earth connection "visible" to the upstream RCD which will still trip because the downstream RCD did not clear the fault.
Although the current will be reduced by tripping the line there will still be transient current flowing possibly from another circuit that can use the earth path.

That was sort of what I was rambling on about in post 5 although I can't see a current flowing from another circuit as, if there was coupling of circuits the RCDs would not like it in the 1st place.

However transients from connected equipment is an interesting one, I can make sense of that, thanks.

So I guess this is saying that (for example) a TT with up front 100/300mA time delay, DP, RCD followed by 30mA RCBOs in the CU might not provide full discrimination. Maybe not a disaster in a general domestic situation but not allowed when discrimination is a safety issue, eg a dangerous situation could be created if another circuit was affected.
 
someone might correct me but I think most domestic RCBOs are single pole. I believe you can get DP ones but I don't think they are common.

I've just been reading a thread about SP RCBOs and the fact they do not break the neutral. The arguement being that this is not much good if it is a N->E fault. I suppose if the upstream RCD is DP and the downstream SP then a neutral to earth fault would trip both of them, meaning you don't have discrimination.

EDIT: thinking more I am still not sure. I am trying to think of a situation where a neutral to earth fault on a final circuit would not be fed by that specific circuits Line, meaning the downstream sp RCBO would effective clear the fault by isolating the line conductor. If the neutral for the whole system is significantly above earth then I would be happy that it needs the upstream RCD to clear it. Not sure if that makes sense.....

I just noticed that assumption and maybe,its not the case
As far as I am aware single pole rcbos can also have a switched neutral,they take up 2 modules, single pole solid neutral are one module
 
I just noticed that assumption and maybe,its not the case
As far as I am aware single pole rcbos can also have a switched neutral,they take up 2 modules, single pole solid neutral are one module

I was referring to single module domestic RCBOs which I believe are solid neutral. Am I am wrong?
 
I can't see a current flowing from another circuit as, if there was coupling of circuits the RCDs would not like it in the 1st place.
If you have a single pole RCBO trip out on a neutral earth fault then, for any other circuits in that board there is still a current path for neutral current (once it has passed normally through its own RCBO (and so not tripping it) to take an alternative route from the neutral bar up the tripped circuit neutral and so via the fault to earth.
If the upstream DP RCD is, well, upstream then the current now flowing to earth creates a L-N imbalance and trips.

Rather vague picture showing a N-E fault not cleared by the first RCBO tripping and the orange line shows a current path that can then bypass the upstream RCD.
[ElectriciansForums.net] 531.2.9 what does it mean?
 
If you have a single pole RCBO trip out on a neutral earth fault then, for any other circuits in that board there is still a current path for neutral current (once it has passed normally through its own RCBO (and so not tripping it) to take an alternative route from the neutral bar up the tripped circuit neutral and so via the fault to earth.
If the upstream DP RCD is, well, upstream then the current now flowing to earth creates a L-N imbalance and trips.

Rather vague picture showing a N-E fault not cleared by the first RCBO tripping and the orange line shows a current path that can then bypass the upstream RCD.
View attachment 18065

Thanks Richard, got it!
 
I think you are wrong and that all Rcd/rcbo's are double pole but please correct me if I am wrong
 
Last edited by a moderator:

Reply to 531.2.9 what does it mean? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
455
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top