M
marshr02
Hi folks. TN-S System with MET near incoming as you would expect. The 10mm2 bonding conductor (gas) passes through the CU to reach the MET due to the physical layout. Is there any reason why it can't be terminated inside the CU alongside the 16mm2 earthing conductor. Obviously testing of earth might be slightly harder. I suspect it may still be worth carrying it to the MET. Cheers