Evening

I am supplying a garage which is 14 meters from the house (House is TNCS), I will be taking the supply from a non - RCD protected 32A MCB using 6mm SWA cable buried. I will not be exporting the earth, so will installing earth rod - TT at the Garage, protected with a 30ma RCD and 2 MCB's 6 & 16amp.

Is is this sufficient protection MCB & SWA or is RCD protection needed?

Where I am confused is the earthing connections from the house as I am not exporting the earth is my only earth connection for the circuit from the earth tag of the SWA.

Also in the garage, I have my earth from the rod connected and the terminal and the earth tag from the SWA.

I originally purchased 3 core SWA and was told I should connect the earth to the house and leave it disconnected at the shed.

Think I have over thought this job and I "cant see the wood from the trees", so hoping for some clarity.

Thanks
 
Evening

I am supplying a garage which is 14 meters from the house (House is TNCS), I will be taking the supply from a non - RCD protected 32A MCB using 6mm SWA cable buried. I will not be exporting the earth, so will installing earth rod - TT at the Garage, protected with a 30ma RCD and 2 MCB's 6 & 16amp.

Is is this sufficient protection MCB & SWA or is RCD protection needed?

Where I am confused is the earthing connections from the house as I am not exporting the earth is my only earth connection for the circuit from the earth tag of the SWA.

Also in the garage, I have my earth from the rod connected and the terminal and the earth tag from the SWA.

I originally purchased 3 core SWA and was told I should connect the earth to the house and leave it disconnected at the shed.

Think I have over thought this job and I "cant see the wood from the trees", so hoping for some clarity.

Thanks

Who told you that?
 
Whats needed is some aluminium framed greenhouse queries with paraffin heaters in them.

Q.
Do I bond the frame to the nearest wet tree?

A.
Why the fXZ! do you need to bond it?

Or similar scenarios:)
 
Whats needed is some aluminium framed greenhouse queries with paraffin heaters in them.

Q.
Do I bond the frame to the nearest wet tree?

A.
Why the fXZ! do you need to bond it?

Or similar scenarios:)

Good question well phrased, however I do not know the answer to this question just now. But I will speak to the knights who say Ni for clarification on shrubberys.
 
Evening

I am supplying a garage which is 14 meters from the house (House is TNCS), I will be taking the supply from a non - RCD protected 32A MCB using 6mm SWA cable buried. I will not be exporting the earth, so will installing earth rod - TT at the Garage, protected with a 30ma RCD and 2 MCB's 6 & 16amp.

Is is this sufficient protection MCB & SWA or is RCD protection needed?

Where I am confused is the earthing connections from the house as I am not exporting the earth is my only earth connection for the circuit from the earth tag of the SWA.

Also in the garage, I have my earth from the rod connected and the terminal and the earth tag from the SWA.

I originally purchased 3 core SWA and was told I should connect the earth to the house and leave it disconnected at the shed.

Think I have over thought this job and I "cant see the wood from the trees", so hoping for some clarity.

Thanks

Seems you believe everything your told, including leaving a perfectly good earth (0.35 ohm) behind, in favour of an unstable 200 ohm earth!! Good luck to you!!
 

Reply to Supplying garage with power in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
461
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

My wife’s Evoque gets about 32 miles on a full charge and I get about 28 miles on my F-Pace. I don’t know how long a full charge takes but I...
Replies
13
Views
1K
Haha yes, it is. Must be a northern expression. Have a Google 😂
Replies
3
Views
343

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top