Called around to recce a job coming up soon for a builder. Looks around house (unoccupied - nice one) things looking good for the extension. Takes a look at at existing bonding cu and supply etc. Noted the clamp on the lead covered incomer, thought thats naughty, and it was 10mm. then followed it up the cu and noticed its chopped. Ahhhh no earth, runs back to van gets tester out.

Then I go to take the lid off and notice 2 rcds, eyesight a bit sh1te but it was 100ma and 30 ma,, ok all the signs now point to TT. checks these 2 x 10mm one was to gas and water continuous bond. the other to a spike. Result Get up ye dancer.

Ze was at 0.18ohms happy with that, and better when it goes to 16mm.

But on a side note why was there a clamp on the supply incomer, I did actually test the lead sheath also to confirm earth path, but there was none. I understand why it was chopped due to twig in garage floor.

But why the use of the clamp in this instance, someone just trying to bond the cable also ??
 
do you think this will make much difference on a TT?
;)
Not over the distance of 2 mtrs no. However there is nothing wrong in striving to get the best reading possible on a TT. Hence more arguments on here accepting anything under 200ohms is fine.

something smells wrong here. i can't see a Ze of 0.18 on a twig, TBH, even if eng54 istalled it. LOL.
Nothing smelly here lol,why not get a good reading like that ive had a few over the years, it is what it is. Been back this afternoon, checked with another mft, and it was 0.19ohms.


it`l be parallel paths here Tel...
No parrallel paths all bonding conductors disconnected at time of testing


Thats why I asked Toonlad if he had taken the earthing conductor out of the MET.
He said he opened the main switch but not answered fully my question.
Like i said i tested it correctly. Granted i did not quote that i had removed the earth from the MET, but testing correctly is removing it,and opening the switch.


I was back this afternoon, the reading is correct, No parrallel paths the neighbours are on TT there spikes in the garage too.

so can we get back to why was there a clamp on the incomer when there is no earth path on it. The best answer has been power ranger thus far.

[ElectriciansForums.net] Yesterdays little heart beat skip
 
Last edited:
Not over the distance of 2 mtrs no. However there is nothing wrong in striving to get the best reading possible on a TT. Hence more arguments on here accepting anything under 200ohms is fine.


Nothing smelly here lol,why not get a good reading like that ive had a few over the years, it is what it is. Been back this afternoon, checked with another mft, and it was 0.19ohms.



No parrallel paths all bonding conductors disconnected at time of testing



Like i said i tested it correctly. Granted i did not quote that i had removed the earth from the MET, but testing correctly is removing it,and opening the switch.


I was back this afternoon, the reading is correct, No parrallel paths the neighbours are on TT there spikes in the garage too.

so can we get back to why was there a clamp on the incomer when there is no earth path on it. The best answer has been power ranger thus far.

View attachment 18586
couldn`t agree with you more....depth of rod/s & suitable siting would be the key here....
 
Not over the distance of 2 mtrs no. However there is nothing wrong in striving to get the best reading possible on a TT. Hence more arguments on here accepting anything under 200ohms is fine.


Nothing smelly here lol,why not get a good reading like that ive had a few over the years, it is what it is. Been back this afternoon, checked with another mft, and it was 0.19ohms.



No parrallel paths all bonding conductors disconnected at time of testing



Like i said i tested it correctly. Granted i did not quote that i had removed the earth from the MET, but testing correctly is removing it,and opening the switch.


I was back this afternoon, the reading is correct, No parrallel paths the neighbours are on TT there spikes in the garage too.

so can we get back to why was there a clamp on the incomer when there is no earth path on it. The best answer has been power ranger thus far.

View attachment 18586
probably had been TT...but was then upped to
TN-S...which has since degraded/broken down....if this is the case then another good argument for having backup with rod/s.....like if a system is upgraded....then leave the rod/s in place...cant halm can it....
 
Sorry about the size of image, should have edit it before uploading.

Glennspark, sounds about right what you said. I just like to get my head around why we get these little scenarios. I feel so epic now. lmao
 
Bloody hell.... as they say.

Old Northern Electric stickers......I've still got a roll of them somewhere with a coil of wire and seals lol
Subbied for them on a 6 month temp contract 24 year ago:).
 

Reply to Yesterdays little heart beat skip in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top