Called around to recce a job coming up soon for a builder. Looks around house (unoccupied - nice one) things looking good for the extension. Takes a look at at existing bonding cu and supply etc. Noted the clamp on the lead covered incomer, thought thats naughty, and it was 10mm. then followed it up the cu and noticed its chopped. Ahhhh no earth, runs back to van gets tester out.
Then I go to take the lid off and notice 2 rcds, eyesight a bit sh1te but it was 100ma and 30 ma,, ok all the signs now point to TT. checks these 2 x 10mm one was to gas and water continuous bond. the other to a spike. Result Get up ye dancer.
Ze was at 0.18ohms happy with that, and better when it goes to 16mm.
But on a side note why was there a clamp on the supply incomer, I did actually test the lead sheath also to confirm earth path, but there was none. I understand why it was chopped due to twig in garage floor.
But why the use of the clamp in this instance, someone just trying to bond the cable also ??
Then I go to take the lid off and notice 2 rcds, eyesight a bit sh1te but it was 100ma and 30 ma,, ok all the signs now point to TT. checks these 2 x 10mm one was to gas and water continuous bond. the other to a spike. Result Get up ye dancer.
Ze was at 0.18ohms happy with that, and better when it goes to 16mm.
But on a side note why was there a clamp on the supply incomer, I did actually test the lead sheath also to confirm earth path, but there was none. I understand why it was chopped due to twig in garage floor.
But why the use of the clamp in this instance, someone just trying to bond the cable also ??