Doing an eicr in a hotel and the maintanence guy asked if i could take a look at an intermittantly tripping rcd.

Rcd tested fine, so i started disconnecting the fittings for an ir test and found this.

[ElectriciansForums.net] I dont think they should look like that


200mm of kingspan, and unenclosed connector blocks sitting in the kingspan directly above a 50w downlight.

Anyone else had any fun findings this week?

Tim
 
Doing an eicr in a hotel and the maintanence guy asked if i could take a look at an intermittantly tripping rcd.

Rcd tested fine, so i started disconnecting the fittings for an ir test and found this.

[ElectriciansForums.net] I dont think they should look like that


200mm of kingspan, and unenclosed connector blocks sitting in the kingspan directly above a 50w downlight.

Anyone else had any fun findings this week?

Tim

At least it's parked between the lines.

And that hr insulation looks brill.
 
Doing an eicr in a hotel and the maintanence guy asked if i could take a look at an intermittantly tripping rcd.

Rcd tested fine, so i started disconnecting the fittings for an ir test and found this.

[ElectriciansForums.net] I dont think they should look like that


200mm of kingspan, and unenclosed connector blocks sitting in the kingspan directly above a 50w downlight.

Anyone else had any fun findings this week?

Tim
just this little bit of nonsense going on in a cellar....
looks like a Electrical Trainee board change....

[ElectriciansForums.net] I dont think they should look like that[ElectriciansForums.net] I dont think they should look like that[ElectriciansForums.net] I dont think they should look like that
 

Reply to I dont think they should look like that in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K
  • Question
My thoughts exactly! Snowed under with work at the moment, so might have to pass it on 😬😬
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top