board change | Page 3 | on ElectriciansForums

Discuss board change in the UK Electrical Forum area at ElectriciansForums.net

G

GLENNSPARK

this is the board change i said i was on with this morning:

[ElectriciansForums.net] board changethis is the intake arrangements for the 4 flats

[ElectriciansForums.net] board changegetting a Ze=0.09

[ElectriciansForums.net] board changethe existing 4 way BS3036 board

[ElectriciansForums.net] board changeold board removed & finals broken out ready for IR and (R1 R2)

[ElectriciansForums.net] board change(R1 R2) at the furthest point on the lighting circuit=1.28

[ElectriciansForums.net] board changenew board going on

[ElectriciansForums.net] board changenew board straight & level minus cover

[ElectriciansForums.net] board changea closer look

[ElectriciansForums.net] board changeall dead testing has been done....IR was good...the lowest came back at
18 meg with nothing borrowed/shared ...now ready for the cover to go on & energise....Zs & RCD then sticker up and clean any mess made before leaving....:wink:
 

Attachments

  • [ElectriciansForums.net] board change
    Picture 004.jpg
    187.5 KB · Views: 338
Nice to see some pics in progress, I'm looking on my phone so quite small pics but in pic 2 doing ZE what is your earth lead connected to? It looks like you haven't disconnected the main earth it looks like your testing all the flats earths? Could be wrong though small pics on phone, you look like that guy who won triple jump at the Olympics ( but slightly bigger :love:)
 
Not a critiscm glenn but how comes you put a main switch and an RCD in?
was just in the board....the board was a split load job...look at the neutral bars....

- - - Updated - - -

Nice to see some pics in progress, I'm looking on my phone so quite small pics but in pic 2 doing ZE what is your earth lead connected to? It looks like you haven't disconnected the main earth it looks like your testing all the flats earths? Could be wrong though small pics on phone, you look like that guy who won triple jump at the Olympics ( but slightly bigger :love:)
yep...well spotted onions....the pic i have allocated the Ze....was in fact the PEFC test....
 
For some reason i always pictured you as a thin wiry guy... lol!! I bet most picture me similar to your build, and probably bald too. How mistaken they would all be!! lol!!

Nice job Glenn, though it would have been better to have kept the bared conductor of the terminated cables to a minimum on the Neutral bar!!
if your on about the 25mm neutrals....they come like that with pre-formed ends...i think the strands are resistance welded together...or brazed or something....and i agree with you on em...their too long.....
 
He just called you fat :)

I think he said something about your mum too!

For some reason i always pictured you as a thin wiry guy... lol!! I bet most picture me similar to your build, and probably bald too. How mistaken they would all be!! lol!!

Nice job Glenn, though it would have been better to have kept the bared conductor of the terminated cables to a minimum on the Neutral bar!!
 
But a ZE not a ZDB
right:
the pic shows me carrying out a Ze to the property....i do this before any board change to confirm there is actually a proper earthing to the property...
now, this being flats after i had confirmed there was a good earth to the building i then got a Zdb at the board before replacing it...
the PFC i put down was the one i got when confirming the Ze in the pic....its going to be higher than the one i get at the board isn`t it...so as far as i`m concerned its covered...
hope this clears up any confusion.
Glenn.
 
Nice to see some pics in progress, I'm looking on my phone so quite small pics but in pic 2 doing ZE what is your earth lead connected to? It looks like you haven't disconnected the main earth it looks like your testing all the flats earths? Could be wrong though small pics on phone, you look like that guy who won triple jump at the Olympics ( but slightly bigger :love:)

Looks like you have lost your marbles again lol
 
I think onions is trying to say your are carrying out a zdb in your photo in your photo it shows all earthing cables to your earthing block, to carry out a true ze there should only be your main earth connected but you know that right lol nice neat job by the way good to see there are still some guys in the trade that take pride in there work :)
 
I think onions is trying to say your are carrying out a zdb in your photo in your photo it shows all earthing cables to your earthing block, to carry out a true ze there should only be your main earth connected but you know that right lol nice neat job by the way good to see there are still some guys in the trade that take pride in there work :)
no..the pic shows me carrying out PFC...thats why all the G/Ys are in the block....the other pic i posted shows me doing a Ze at the intake position....
i then went on to get a Zdb at the board .....
 

Reply to board change in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top