well...here I am again...this time its installing a TT system utilising 2X 5/8" rods...with the connector..:
here is the necessary gear as laid out (the 20mm PVC conny isn`t in the pic)
these are the type of rods you need...no 3/8" twigs here (apart from in that bush behind maybe)
site is about 1 1/2 meters away from the house...thats the first one in..now to connect the second onto the first ....and carry on...
still some way to go...
get it brayed in....Robert my assistant uses the fork with a bit of tape to keep the rod steady
thats a length of 10mm CSA G/Y being pulled through a length of conny for main earthing (the conny was dropped into the ground)
Ze was OK at just over 15 ohms...had to change the 16th edition setup in the board...it was configured as a split load 10 & 2....dropped another RCD in it and did it 5 & 5
happy days...:biggrin: