Hi folks
testing an old victorian townhouse today and found the DNO cutout as shown in the photo. the make is Asco, never seen one this old before.
it appears to be TNC-S (the first way is not used). At the head with test leads connected to line and neutral/earth linked i measured 0.20 ohms, which is acceptable but at the DB i measured 4.50, it seems there's no earth cable from link to DB. there's no bonding in the house either main, supplementary or otherwise.
anyone else found this. I'm guessing it was rewired in mid 60s due to style of wylex DB.[ElectriciansForums.net] help with old style head
 
nothing about the antics of DNOs is puzzling. they make up the rules as they go along up until friday lunch time. then anything goes as long as they can knock off on time.
 
From the age of the head I would have expected a TNS system, but it looks like there is no earth so is there an earth rod elsewhere?
Is there any sign of an old earth connection from the incoming sheath?
It is possible it was a fused line and neutral at one point and the neutral was redirected when the tails were changed.
 
i thought it was tncs because of the little green box at the side of the big one. its the same make and age as the big one. thought there might have been a connection between the lead sheath and neutral. can't find a rod anywhere, maybe it was/is connected to water main?
 
I saw exactly the same head in Harrogate the other day - Line was fused at "something amps" - Electrician could not get it out without fear of breaking it and the N was just a link (or a high current fuse lol). earth was on lead sheathing TNS and beautifully educational as you dont see many TNS here. DNO after eighty phone calls are going to replace it though.
 
i thought it was tncs because of the little green box at the side of the big one. its the same make and age as the big one. thought there might have been a connection between the lead sheath and neutral. can't find a rod anywhere, maybe it was/is connected to water main?


The cut-out may well have been adapted to cater originally for a 2 phase + N!! When this Cut -Out was being installed, i doubt very much if anyone would have heard of PME/TNC-S.

Where is the earth linked to the neutral that you talked about testing, as i can't see any main earthing conductor leaving this cut-out???
 
what puzzled me also is that there was a DNO sticker on the DB dated 2009 where they've fitted new tails and a 60947-3 switch!
So why have you opened up the cut out? I can see bitumen leaking below the fuse carrier, was this still soft? Could be a slack connection. Call the DNO ASAP.
 
So why have you opened up the cut out? I can see bitumen leaking below the fuse carrier, was this still soft? Could be a slack connection. Call the DNO ASAP.

That's not leaking, that's roughly the expected bitumen pitch level you would see in one of these older pitch filled cut-out heads...
 

Reply to help with old style head in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
474
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top