Hi folks
testing an old victorian townhouse today and found the DNO cutout as shown in the photo. the make is Asco, never seen one this old before.
it appears to be TNC-S (the first way is not used). At the head with test leads connected to line and neutral/earth linked i measured 0.20 ohms, which is acceptable but at the DB i measured 4.50, it seems there's no earth cable from link to DB. there's no bonding in the house either main, supplementary or otherwise.
anyone else found this. I'm guessing it was rewired in mid 60s due to style of wylex DB.
testing an old victorian townhouse today and found the DNO cutout as shown in the photo. the make is Asco, never seen one this old before.
it appears to be TNC-S (the first way is not used). At the head with test leads connected to line and neutral/earth linked i measured 0.20 ohms, which is acceptable but at the DB i measured 4.50, it seems there's no earth cable from link to DB. there's no bonding in the house either main, supplementary or otherwise.