i would agree but the current code of practic is
Code 1 (Requires urgent attention)
This code is to be used to indicate that danger exists, requiring urgent remedial action. The persons using the installation are at risk. The person ordering the report should be advised to take action without delay to remedy the observed deficiency in the installation, or to take other appropriate action (such as switching off and isolating the affected parts of the installation) to remove the danger. The inspector should not wait for the full report to be issued before giving this advice. As previously indicated, some certification, registration and membership bodies make available ‘Dangerous Condition’ notification forms to enable inspectors to record, and then to communicate
immediately to the person ordering the report, any dangerous condition discovered.
there for items such as
Exposed live parts that are accessible to touch,
such as where
a fuse carrier or circuit-breaker is omitted from a consumer unit and a blanking piece is not fitted in its place
terminations or connections have no (or damaged) barriers or enclosures, such as those belonging to a consumer unit
live conductors have no (or damaged) insulation
an accessory is damaged.
Conductive parts that have become live as the result of a fault
Absence of an effective means of earthing for the installation
The main RCD or voltage-operated earthleakage circuit-breaker on a TT system fails to operate when tested with an instrument or integral test button
but there is nothing about the risk or burns due to heat from a oven ?? so i still think a code 2
Code 2 (Requires improvement)
This code is to be used to indicate that the observed deficiency requires action to remove potential danger. The person ordering the report should be advised that, whilst the safety of those using the installation may not be at immediate risk, remedial action should be taken as soon as possible to improve the safety of the installation.