have to re wire an industrial unit and surrounding work shops but in two minds of how to install
currently there is NO EARTH for the whole site, the place consists of a large storage shed with the mains coming in, TPN 100a supply, the place at the moment is a death trap
no current RCD protection at all(not that it would help with there being no earth)
Loop test between L1/2/3 and N is 0.57ohms and has been confirmed no PME connection is available
4 surrounding buildings rented out, few workshops, 1 mechanics hut, mainly lighting and sockets with 2x tpn hydraulic ramps, no major loads
proposed new install will be
TPN dist boards in each building, 16mm swa submains from each outbuilding back to 63a switchfuses via 100A busbar to origin
my plan was to have a 300mA s type 4 pole RCD at scource with earth rod 2x large coupled together
either 30mA rcd main switches at all distribution boards, or mainswitch isolators and 30mA DP rcbos for additional protection as required
thing is im a bit nervous about this install as i know whatever set up i choose nusiance tripping is likely in the future and may take out the whole site in some cases, so im leaning towards the 30ma RCD mainswitch at each dis board so i can at least keep a fault from knocking out all the sites at once and keep it local to the building affected
most of the existing final circuits are staying for now(i am pushing for a full site re-wire but have to start at the distribution for now)and there are lots of bodges and add ons all over the place
i have made agreements with the landlord to correct C1 and C2 faults with the testing as i find them at extra cost
have a feeling this one will bite me on the bum in the future
any input? have i missed any thing that could improve the RCD set up or other suggestions?
currently there is NO EARTH for the whole site, the place consists of a large storage shed with the mains coming in, TPN 100a supply, the place at the moment is a death trap
no current RCD protection at all(not that it would help with there being no earth)
Loop test between L1/2/3 and N is 0.57ohms and has been confirmed no PME connection is available
4 surrounding buildings rented out, few workshops, 1 mechanics hut, mainly lighting and sockets with 2x tpn hydraulic ramps, no major loads
proposed new install will be
TPN dist boards in each building, 16mm swa submains from each outbuilding back to 63a switchfuses via 100A busbar to origin
my plan was to have a 300mA s type 4 pole RCD at scource with earth rod 2x large coupled together
either 30mA rcd main switches at all distribution boards, or mainswitch isolators and 30mA DP rcbos for additional protection as required
thing is im a bit nervous about this install as i know whatever set up i choose nusiance tripping is likely in the future and may take out the whole site in some cases, so im leaning towards the 30ma RCD mainswitch at each dis board so i can at least keep a fault from knocking out all the sites at once and keep it local to the building affected
most of the existing final circuits are staying for now(i am pushing for a full site re-wire but have to start at the distribution for now)and there are lots of bodges and add ons all over the place
i have made agreements with the landlord to correct C1 and C2 faults with the testing as i find them at extra cost
have a feeling this one will bite me on the bum in the future
any input? have i missed any thing that could improve the RCD set up or other suggestions?