have to re wire an industrial unit and surrounding work shops but in two minds of how to install
currently there is NO EARTH for the whole site, the place consists of a large storage shed with the mains coming in, TPN 100a supply, the place at the moment is a death trap
no current RCD protection at all(not that it would help with there being no earth)
Loop test between L1/2/3 and N is 0.57ohms and has been confirmed no PME connection is available
4 surrounding buildings rented out, few workshops, 1 mechanics hut, mainly lighting and sockets with 2x tpn hydraulic ramps, no major loads
proposed new install will be
TPN dist boards in each building, 16mm swa submains from each outbuilding back to 63a switchfuses via 100A busbar to origin
my plan was to have a 300mA s type 4 pole RCD at scource with earth rod 2x large coupled together
either 30mA rcd main switches at all distribution boards, or mainswitch isolators and 30mA DP rcbos for additional protection as required
thing is im a bit nervous about this install as i know whatever set up i choose nusiance tripping is likely in the future and may take out the whole site in some cases, so im leaning towards the 30ma RCD mainswitch at each dis board so i can at least keep a fault from knocking out all the sites at once and keep it local to the building affected
most of the existing final circuits are staying for now(i am pushing for a full site re-wire but have to start at the distribution for now)and there are lots of bodges and add ons all over the place
i have made agreements with the landlord to correct C1 and C2 faults with the testing as i find them at extra cost :)
have a feeling this one will bite me on the bum in the future
any input? have i missed any thing that could improve the RCD set up or other suggestions?
Hi,
Just a few thoughts to get things going.
To try and rectify something that is not satisfactory is far harder than trying to install from scratch. At least with a rewire a proper design and layout can be put in place which would be far superior to what you have now. Personally I don't like the idea of 30mA up front especially for Workshops and ramps, Yes for the circuits deemed necessary but not at the DB.
As for the TT Earthing, shout loud enough and E54 may hear you, he's your man for this.
Regards.
thanks for the input
eventually the site will be fully rewired as there has already been one serious fire due to overload on cables too small and fuses too big
i have to get some pics of this place its UNBELIEVABLE!
but we have to start on the submains and switchgear as this is the worst and work outwards
but regarding the new install, i really dont want to protect a whole board with 30mA up front, its a crap design but, not much options
but at the same time i dont want a small fault on one building to take out everyone
and the kind of stuff they are using, is prone for problems
its a bit of a ballache tbh
This isn't a Domestic installation, ....you'll be needing a bit more than a couple of coupled 5/8'' rods on this installation!!
You'll be needing that sort of arrangement at each of the buildings and those rod positions linked out. What sort of building construction type are we talking about here steel framed, concrete framed brick infill, brick built or other?? Whereabouts in Essex is this industrial site??
Anyway, i'll get back here later after work, no time right now...
Just my two cents, I will say this and this alone; on a TT like the one you have described, I would be banging in linked rods at least 16ft until I was achieveing a very stable TN value Ra at the origin of supply. 2 coupled rods just won't cut it I'm afraid.
This thread is going to get rather long winded from now on as every man and his dog tries to pipe up with RCD this and RCD that. Enjoy! :D
an earth nest....
I'd start by knocking in a sample rod, maybe 3 x 2.3meter rods coupled together then do an Ra test. Until you get some info about the ground you're working with it's difficult to come up with a final plan or price for that matter. I'd also be looking at ways to incorporate the building and foundation steel work.
well....theres the other way as well...
its called `specific ground resistance testing`....here:
I think you're talking about measuring ''soil resistivity'', which will give you a good idea of what the surrounding soil is going to provide, as far as earth rods and the like. Unfortunately you're illustration is for a standard 3 point Ra measuring situation. Measuring soil resistivity is always via 4 points typically using the Wenner or Schlumberger method....
yes sorry eng....the image i posted is indeed Ra testing....this is more like it:
Skelton, good question. I was told whilst doing 2395 a bit back exactly that with detached steel buildings. I don't know the reason for this though. I was trying to take in everything else!
im not overly concerned at this point about the rods, the soil around most of the area i live is dense clay, i hardly ever get reading above 25ohms with a decent length rod even in the mid summer months, the moisture in the clay is pretty constant once you penetrate to a certain depth, also the structural steel will obviously be main bonded too so a stable RA will likely not be an issue, and i have left a margin in the price for any problems
its the rcd configuration i was more concerned about
Whoever was telling you that is talking rubbish. The only reason I could see the need to separate the earthing system for a detached steel outbuilding and provide it with its own TT is if the main supply is PME.
Get TN values then your RCD configuration becomes less of a worry.
Me personally, I'd be banging in rods until I got a good 0.5 ohms, lower if possible and scrapping the idea of an RCD altogether on the main distribution arrangement, depending on how happy I was with the stability of the Ra value would determine whether or not I would protect each sum main with a type-s, then I'd just be worrying about the 30mA RCDs needed on the finals for additional protection if needed. If like you say the area is dense clay then a sub one ohm Ra value is a piece of cake. I reckon three or four starlinked 16 footers would do the job perfectly!
Once done I'd be monitoring the Ra monthly for about a year to be sure of its stability.
One thing is for sure, I'd rather have one strong earthing arrangement at the origin of supply and an exported earth to each outbuilding than a bunch of weak seperate TTs at each outbuilding relying on their own RCD protection to meet the requirements for ADS.
I must admit i have never even tried to achieve TN levels of RA, not really considered it an option before
thing is it must be a bit risky, as if due to corrosion or whatever other reason, maybe in years to come, the RA was to raise a little, theres not much of a margin before all my ZS values are exceeded and the whole install will become a hazard
i dont think i would rest easy with that, its too tight, and the zs values for my submains BS88 fuses at 63A is only 0.82ohm with no Correction, ive got to include the runs of cable on top of that too
and i dont really have an option to protect each submain independantly either with an s type, as there will be four switch fuses from a busbar, so will need to get the s type before all that
The Ra will only decrease over time due to ground consolidation and will not increase, the corrosion you speak of, although highly improbable would be picked up upon correct periodic inspection too. A correctly installed TT system whereby the main aim is to keep the ohmic value of the earth fault loop path as low as those seen in TN systems will be in 99% of circumstances MORE stable and safer than either TN earthing arrangements. I have personally seen TT systems with Ra values as low as 0.2 - 0.3 ohms and that aint easy considering the ground where I live (solid chalk) and I'm sure there are plenty of us on here who have seen waay lower than that! If your install is on solid clay, you should expect to be getting these sort of results with relative ease. Remember also that if you are achieving TN values, if ADS is being met by overcurrent protective devices then you are permitted to apply TN disconnection times too.
I personally think that relying on one RCD, type-s or not, to protect the entire installation is just asking for trouble and in my opinion is bad design. I would be more than happy to rely on a stable TN Ra value to protect the main distribution arrangement.
If you're used to working in the domestic/light commercial field then trying to achieve TN Ra values is just simply not cost effective and I could understand perfectly in those circumstances why someone would not want to try to achieve such a low Ra value, but in the circumstances that you are talking about I would say it would be improper to do the job any other way than the way I have already mentioned (short of relying on a different protective measure altogether).
Ive not installed many earth rods. The only ones ive installed was when I was an apprentice and it was just the single rod knocked into the ground using the small black conduit box cover
just interested in hearing how others install pits and rods.
also interested how you star link several rods I know you have to knock them in at certain distances apart otherwise they are pointless. What I'm interested in is how you link them together do you run conduit in between them and link all
[QUOTE. I don't know the reason for this though. I was trying to take in everything else![/QUOTE] Advice given but the reason behind the advice is not known. Priceless.
as I and others have already said here:
depth is the ticket....
the only way to ensure stability in all weather conditions...
This is a proper earth pit:
It is important to note that this isn't the usual chang wang piece of excrement peddled by some electrical wholesalers which is essentially a cheap plastic box with a sticker on it like the one you describe. For a TT system where you want to achieve TN Ra values, unfortunately the 3/8" 4ft rod just won't cut it I'm afraid (I'm not bad mouthing the 3/8" rod [or the twig as it is often described], I'm purely stating that it isn't suitable for this task). You would need to use a 5/8" rod, some are sold at lengths of 12ft but more likely you will find them 4 ft in length but with the ability to couple to other 5/8" rods by using an earth rod coupler. This way you can achieve great depth and very stable results.
This is how I would star link more than one rod (apologies for the rather rudimentary drawing):
I must note that there are many more methods available when it comes to linking rods together however in many cases the method used to link them together is often down to personal preference and often down to common sense. I prefer this method over just linking from one to the next in case the link between the first rod and the MET gets broken somehow leaving the installation unearthed! It also keeps the resistance of the main earthing conductors low as it uses four shorter lengths instead of one long linked length.
If a main earthing conductor is not mechanically protected then it should be buried at a depth of at least 600mm and must comply with 542.3.1, in particular it must be sized in accordance with table 54.1.
The key to achieving effective earthing in a star linked configuration is to ensure that the distance between each seperate rod is at least ten times the length of the longest rod so as to prevent any rod from intefering with another's zone of influence. For example, if you have coupled four 4ft rods (a total of 16ft length) and sunk them in and repeated this three more times (four seperate 16ft rods linked together) then the distance between that and any other rod should be at least 50m.
Hope this helps explain things a bit better.
Advice given but the reason behind the advice is not known. Priceless.[/QUOTE]i think what Damian is getting at Trevor by star connecting the earth nest is to introduce multiple parallel paths thus bringing down yet further the value of Ra...
as opposed to series connected...
The key to achieving effective earthing in a star linked configuration is to ensure that the distance between each seperate rod is at least ten times the length of the longest rod so as to prevent any rod from intefering with another's zone of influence. For example, if you have used four linked 4ft rods (a total of 16ft depth) then the distance between that and any other rod should be at least 50m.
yep...its all about spheres of influence here...
overlapping spheres being an inefficient way of installing rods...
It wasn't Damian I was quoting, it was someone who he had pulled for giving silly advice. I've a lot of time for Damian because he talks a hell of a lot of sense.
By the way, I completely understand the concept of earth nests,multiple parallel paths and TT systems Glenn, I've been doing this a long time.
that was ignorant of me Trev.
sorry mate.:wink:
That Is really good and clear :-) thanks for the info
As you state I have only come across the twig rods this was all that was supplied when I was training and carrying out domestic rewires
I can rember learning about earth rods at college and that they have to be installed at a distance of ten times the length of the rod to make sure that the zones don't interfere with each other
With regards to the earth pit I take it you dig a hole to sink the cover so it's level with the ground and then install the rod into this.
I also guess the reason for the pit is to provide a means to inspect the rod and connection when carrying out inspection and testing in the future
Thanks for the diagram of star linking rods it makes it clearer
I can see why it's better to run seperate cables to each rod rather than link all 4 with one cable
Can I just ask would you just install the cables direct in the ground at greater than 600mm or do you install mechanical protection using galv conduit or ducting ?
Thanks for the info and taking the time to share your wisdom it's really useful and good to know for future should I have to install a TT system
I won't be installing any more twigs
Agree with Mr Skelton to a large degree here, but i'd personally also have a rod position at each of the major buildings that would be linked back to the building containing the the incoming supply. I say this, because any of those sub-main cables to the other building can be interfered with at any time in the future, and through negligence or incompetence loose that substantial TT earthing arrangement at the main intake building. Those extra rod positions will also help lowering the sites overall Ra value.
Easy to check if these metal framed buildings are providing decent levels of Ra values. I'd bond them to the buildings MET/EMT at two diagonal locations as a matter of course anyway.
Any TT system that has been well thought out and installed will have a minimum of 30 years lifespan and more often than not considerably more. Depends very much on the soil make-up and whether these industrial units have been used for storage and affected by long term spillages of corrosive chemicals in the past.
As been stated, once you have attained stable TN values there is nothing ''risky'' about it. The RCD issues will indeed become far less of an issue. You basically treat the installation as a normal TN-S supply throughout!! If i were to include an up-front RCD, it would be more like a 500mA value than a 100/300mA, but if you attain a very low Ra value you really won't need anything, and you could actually be incorporating a nuisance tripping factor!!
On a final note, rather than not being ''Overly Concerned'' about the rods and earthing, this should initially be far more of a priority. Once you know what sort of Ra levels you have, then that is going to relate back to the whole installation, in terms of what you're going to need to supply in terms of protection etc!! I hope you have a decent SDS you can use to drive these rods into the ground?? lol!! Make up an adaptor by welding an old suitably sized socket that fits the rods driving bolt to an old cut off SDS chisel. It will cut rod driving time to a fraction of driving rods by sledge/lump hammer!! lol!!
Easy to check if these metal framed buildings are providing decent levels of Ra values. I'd bond them to the buildings MET/MET at two diagonal locations as a matter of course anyway.
just got there first eng....lol...
Yep, pretty much.
And also to prevent corrosion at the point of connection to the rod.
It all depends on the scenario, for the short domestic run to one rod then I'd normally use galv conduit for protection underground or clip the cable above ground, for a larger job that requires a star linked configuration I'd more likely be burying the earthing conductors deeper but without protection.
Twigs have their uses. Some may disagree as this is a hot topic often debated on here but if you have decent enough ground and some back up protection from a type-s then I wouldn't normally object to the the use of a twig for some types of installation (99% of the time they will be domestic of some sort, ie sheds and garages etc..). I personally will always use two coupled rods to guarantee a further level of stability (solid chalk where I live), but if I'm honest, I do this because I can, I have a ground rod driver and a demo hammer drill so driving two rods takes about 30 seconds, if I tried this with a twig it would just bend.
A very valid point here if you're looking for that extra security factor. Cost allowing, I'd agree wholeheartedly.
Or just buy an earth rod driver lol, they're only thirty squids!
Going to have to disagree with you here, 10 times the driven depth is way OTT. You will achieve little to nothing by going over 3 times the driven depth!! A star connected rod arrangement is normally called a ''crows' or ''birds'' foot, and will consist one central rod, with three rods going off at angles in the shape of a birds foot, keeping a suitable distance between each rod. The three outer rods connect to the central rod, which in turn is connected to the MET of the building.
EDIT.... Should also point out that ''star'' and other similar layout systems are generally only used when and where space is restricted...
On your drawing, you will probably be better off running a buried (600mm depth) bare cable around the house (at least 1m out) connected to an earth rod at each corner.
Not really considering we're only talking about a 30m run from the main intake to each rod. For a site this size I'd say it was fine. That's my opinion anyway, it's what I was taught as a lad, it's what I have always done and it's what I will continue to do.
Any links to further info about the subject of muliple earth rod installations and the most effective distance between them would be much appreciated though. I'm not too stubborn to learn why what I'm doing is OTT if indeed it is! :)
Essex
TT system what set up would you use
Welchyboy1,
D Skelton,