Got a house divided into 3 flats.
3 phase supply but don't want to get a 3 phase board as the smallest is 12 ways (SP) when I only need 4 ways (SP).
Seen a hager enclosure that will take a 3 phase incomer and using a 3 phase busbar I could fit the necessary MCBs/RCBOs. Trouble is that I really want to supply the flats with a 63A supply using the current 16mm T & E, at least one of the cables will need to be RCD protected but hager only go up to 50A for a RCBO. Supplier is saying fit a Protek 63A RCBO, but don't really want to mix different manufacturers.
Would a 50A supply be Ok for the following?
8.5kW Shower
4 ring hob + oven
ring main with about 8 double sockets and at least one 2kW heater
2kW water heater
Lights
It darkest winter I could foresee heater on (8A), water heater on (8A), shower on (37A) and then it only takes a 2nd person to put the kettle on or a 2nd room heater plugged in and thats your 50A+ taken.
Opinions?
3 phase supply but don't want to get a 3 phase board as the smallest is 12 ways (SP) when I only need 4 ways (SP).
Seen a hager enclosure that will take a 3 phase incomer and using a 3 phase busbar I could fit the necessary MCBs/RCBOs. Trouble is that I really want to supply the flats with a 63A supply using the current 16mm T & E, at least one of the cables will need to be RCD protected but hager only go up to 50A for a RCBO. Supplier is saying fit a Protek 63A RCBO, but don't really want to mix different manufacturers.
Would a 50A supply be Ok for the following?
8.5kW Shower
4 ring hob + oven
ring main with about 8 double sockets and at least one 2kW heater
2kW water heater
Lights
It darkest winter I could foresee heater on (8A), water heater on (8A), shower on (37A) and then it only takes a 2nd person to put the kettle on or a 2nd room heater plugged in and thats your 50A+ taken.
Opinions?