I am installing a cooker in a commercial premises and I am new to installations and trying to use the regs (17th) to do it. I have a 7.9KW oven which is 42m from the dist board. I am trying to calculate Ib whereby I have 16 cables coing out of the board but it is possible to run the cable in a false ceiling away from these. Do I need to use Cg for 16 cables or not?

Also, I am passing through 100mm of insulation in a partition, do I need to use Ci for 100mm? The reason I am asking is the calculations have resulted in me requiring a 50mm cable which of course is impossible.

I also understand that I will need a C40A RCBO as the board is not RCD protected? I hope I am not too far off the mark.

Please help!!
 
is 7.9KW the total load? if so, then apply diversity to get your Ib . 6mm cable on a 32A MCB will handle the current. but do a VD calc. for that length of run. secondly, is RCD protection required under 522.6.101?
 
You should use Ci for cables through 100mm of insulation. Check out Table 52.2 (page 129 BGB). Your derating factor is 0.78.
 
is 7.9KW the total load? if so, then apply diversity to get your Ib . 6mm cable on a 32A MCB will handle the current. but do a VD calc. for that length of run. secondly, is RCD protection required under 522.6.101?

Thanks Telectrix, yes that is the total load. Unfortunately it isn't possible to get conduit etc into the wall but I may be able to install it within the parameters of 522.6.101 (v). This is going to sound like a stupid question but could you possibly explain what you mean by diversity? As I said, I'm new to this!!
 
Do I need to use Cg for 16 cables or not?

Yes -- if you've grouped them in a big bunch ?!?!

No -- if you can keep the cables a distance of 2 x their diameter apart.

Practically you are probably going to group your cables in bunches so just use the Cg for that particular group

..... and while Im thinking of it Im sure there is something else about if a cable carries less than 40%(?) of the groupings current you can discount it for grouping purposes --- check the notes in the BGB its hidden in the grouping table!
 
Passing through 100mm/10cm of insulation, i wouldn't dream of derating a suitably sized cable for that sort of distance. Having said that, if you can get a cable to pass through a partition wall then you can surely get a conduit in, to span the partitions wall boards!!
 
.. and while Im thinking of it Im sure there is something else about if a cable carries less than 40%(?) of the groupings current you can discount it for grouping purposes --- check the notes in the BGB its hidden in the grouping table!

30% mate. Just found it. Table 4C1 note 9. (page 327)
 
Passing through 100mm/10cm of insulation, i wouldn't dream of derating a suitably sized cable for that sort of distance. Having said that, if you can get a cable to pass through a partition wall then you can surely get a conduit in, to span the partitions wall boards!!

just what i was thinking. for the sake of 4", rip a handful of the crap out and bang in a short length of tube.
 
Thanks Telectrix, yes that is the total load. Unfortunately it isn't possible to get conduit etc into the wall but I may be able to install it within the parameters of 522.6.101 (v). This is going to sound like a stupid question but could you possibly explain what you mean by diversity? As I said, I'm new to this!!

I know that you're young and keen, but are you suitably trained to carry out this kind of work?
 
cooker diversity. calculate the total rated current from the kW. say that comes to 40A. so applying diversity, you allow for 10A + 30% of the remainder ( in this case 30% of 30A ), so 10A + 10A = 20A ( add 5A id the cooker point incorporates a socket outlet. ). this diversity is to allow for the fact that not all elements will be on at the same time as they are thermostatically controlled and switching on and off during cooking.
 
cooker diversity. calculate the total rated current from the kW. say that comes to 40A. so applying diversity, you allow for 10A + 30% of the remainder ( in this case 30% of 30A ), so 10A + 10A = 20A ( add 5A id the cooker point incorporates a socket outlet. ). this diversity is to allow for the fact that not all elements will be on at the same time as they are thermostatically controlled and switching on and off during cooking.

Thanks a lot mate. Can diversity be applied to all installations? If so, is it the same formula?
 
I know that you're young and keen, but are you suitably trained to carry out this kind of work?

Well, you may be able to help me with that. I trained originally as an Electrical Maintenance Engineer and did my 4-year apprenticeship at college. Since then I have worked alongside Installation sparks and even worked overseas in construction. As far as the practical work goes, I am fully competent. I have just completed my 17th Edition and I due to start my 2394/2395 in January. Do you know what else I need to do to be fully qualified without doing 2-4 years at college in installation?
 
Thanks a lot mate. Can diversity be applied to all installations? If so, is it the same formula?

Do you have a copy of the On-Site Guide? There is a section on diversity in there. Appendix A.
If you don't then PM me your email address and I will email the section to you. The book is worth getting, its a good little book.
 
Well, you may be able to help me with that. I trained originally as an Electrical Maintenance Engineer and did my 4-year apprenticeship at college. Since then I have worked alongside Installation sparks and even worked overseas in construction. As far as the practical work goes, I am fully competent. I have just completed my 17th Edition and I due to start my 2394/2395 in January. Do you know what else I need to do to be fully qualified without doing 2-4 years at college in installation?

I too trained as an electrical maintenance engineer with 4 years at College and all that jazz. What surprises me is that in all that time, you've never heard of diversity. I think you are smiling right now ;)
 
here. y'are:


[ElectriciansForums.net] Cooker
 
basically it's just using common sense, estimating the actual current drawn when not all loads will be switched on simultaneously. for example, if you add up all the MCB ratings in a CU, you may get a total of 250A, but in actual fact, the load on the supply will be only be around 60A.
 
hi mate
your lucky then because i qualified a couple of years ago and in the final year there were loads of diversity calculations e had to do and quite a few diversity questions popped up in my exams.
 

Reply to Cooker in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Is the supply capable of 5*32 = 175A? If 60-100A SP domestic you could never run all at max for any length of time anyway! As above, generally...
Replies
10
Views
2K
  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K
  • Question
Thank you for fast response. The reason I asked is because I had read elsewhere online: "Electric ovens have a wattage rating that tells you how...
Replies
2
Views
1K
  • Question
Yes agreed this is definitely out of my comfort zone and it was from the start. Connecting the lights on to scaffold just had me on edge. So the...
Replies
13
Views
1K
  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks