i'd switch them in pairs then. so only a 4 gang switch. K.I.S.S. is what my old man taught me.
 
I still struggle to see how the lighting and ring main will pass each other in the tube and you will have met regs regarding factors, sounds like you need a 2x2 glav trunking running around at high level and conduit drops, may be worth replanning the whole scheme to be honest, or perhaps you can explain your thoughts about how you intend to wire this so we can understand a bit more about your design.

Ok, ring is 4 x 2.5mm -> 4 x 30 = 120 cable factor
This needs to run past the supply to last two lights which is 3 x 1.5mm (N + 2 switched lines) -> 3 x 22 = 66 cable factor
That's a total cable factor of 186 (the ring does not need to run past the grid switch)

20mm conduit allows 10m for 1 bend, 5m for two bends and 2.5m for three bends.

I could just keep the two conduits running in each direction separate, they would pass / run along side each other at the far end, but given that all the cables there would fit in one conduit I thought that wouldn't be necessary.

Go on, I know I've probably set myself up for a fall now :army:
 
Last edited:
Fair enough Tuttle if you have gone to the trouble of calculating everything then it may well be fine, to answer your question, feeding the ring from one end of the conduit and then out the other is fine, or wire it as Tel mentioned, one leg to odd sockets one to even sockets and link between the last 2, that is what I normally do, either way it is fine.
 
maybe not a fall, but a bit of over complication. still, a slong as it complies, it's you job at the end of the day, so do it as you think fit.
 

Reply to RFC in Steel Conduit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
223
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
683
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
625

Similar threads

And if it's a garage then use metal clad accessories.
Replies
5
Views
405
I can't help wondering about earthing arrangements and how important aesthetics really are when attempting to make the best of a less than ideal...
2
Replies
21
Views
1K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top