Hello I have installed a 100amp contactor in a generator control system I have designed tested and installed
its a simple basic design
two 230v ac contactors controlled individually by 12v 250v contact relays (12v relay used to get away with a cat5 between shed and house) and to change it all over a 230v coil Dp dt relay so when the generator is running the supply is disconnected and the house runs off the generator regardless wether the mains is live or not and disconnects when the generator is off to protect the generator

but the issue I'm having is the contactor on the mains side is humming or buzzing (how ever you would like to put it)
quickly got a app for an idea of how loud the noise is and got arround 30-40 db
the contactor is a abb b50 100a contactor it doesn't do much switching it's pretty much engaged all the time and when i press hard on the test button for dead testing the hum reduces, it's defiantly not arcing

is there a way I can reduce the noise?

Thanks bernie
 
Check the faces of the magnetic core which come together are clean, just a little bit of dirt can cause the contactor to buzz.
Also If the core has not been wound tight then you will get the plates vibrating, the only real answer is to replace in this case.
 
If you have designed and installed this changeover system yourself, i hope you have also mechanically interlocked the mains and generator contactors.

Many things can cause a contactor or relay to buzz, those that have been stated above, to being fixed on an uneven surface, strain being asserted, loose fixings ...and so on.
 
I would also like to see a wiring plan too out of interest to ensure you haven't set yourself up to a having the generator fly through the wall if if you have a mechanical failure like a jammed contactor... when you put the national grids almost unlimited power against the unsynchronised very limited genny supply.... you ever seen a motor stop instantly :shocked3:.

As for the noisy contactor ... many from coil voltage too low to dirt ingress as mentioned above.
 
What they said, plus if you have a mechanical interlock check that it is positioned correctly and not preventing free movement of the contactors.
 
I'll get a picture up soon lost the original drawing which resembled a snakes wedding being only a first draft and made improvements to it as I built it will also throw in pictures of the units
and I do see you concern dark wood I could put in place a safety measure where if the main contactor ever sticks on the generator will not start up when the start button is pressed on the control board
 
Yeah my dad wanted a change over switch but the cost for one was daft and was big and bulky and would have had to run annother armoured cable to the shed so would have cost over£200 just for materials so far I spent half that and all my mother needs to do is start the generator and it'll change over automatically as my mother isn't electrically minded and don't fancy her calling me at work to tell her how to change it all over
 
Here's the new circuit diagram it's incomplete but there's enough there to get a idea of how it's controlled everything has a illumination I.e neon for mains power, neon for genny power, led for mains contactor closed, led for genny contactor closed, led for internal transformer and a led for the back up relay for over night power if a prolonged power cut is in effect

[ElectriciansForums.net] Noisy contactor
 
I'll get a picture up soon lost the original drawing which resembled a snakes wedding being only a first draft and made improvements to it as I built it will also throw in pictures of the units
and I do see you concern dark wood I could put in place a safety measure where if the main contactor ever sticks on the generator will not start up when the start button is pressed on the control board

Putting a simple aux contact won't comply just to risk assessment as others have said you need a mechanical interlock as well as electrical isolation to coils if one fails the other is there for redundancy.. and the mechanical interlock is very reliable obviously routine inspections will back up any possible issues that arise.
 
No offense but you have no concept of how to draw wiring diagrams its over complicated almost impossible to follow and ive had the pleasure of using old Italian and Russian machine schematics without knowing the lingo and trying to establish old symbols so usually im good at deciphering this kind of stuff.
 
I know the difference between a block, wiring and circuit diagram
I purposely put the circuit diagram up to show each component how there connected and how they work a wiring diagram wouldn't show any other information other than where to connect the cables to the components and to the printed circuit board connectors in my system
I can make a wiring diagram but it's not going to give anywhere near the information as my circuit diagram if that's Easyer for yourself
 

Reply to Noisy contactor in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Try disconnecting the "central heating off" wire from terminal 2 and insulate it (eg Wago connector or choc block or similar) and tuck it out of...
2 3
Replies
32
Views
3K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top