RCD 0.0s?? | on ElectriciansForums

Discuss RCD 0.0s?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

L

Loopytunes

Hi all,

Just back from an EICR where one of the RCDS was testing out at 0.0ms for the 1/2, 1 and 5 tests both ways, not had this problem before, can anyone shed any light?

Thanks in advance,

Loops
 
[ElectriciansForums.net] RCD 0.0s??
Hi all,

Just back from an EICR where one of the RCDS was testing out at 0.0ms for the 1/2, 1 and 5 tests both ways, not had this problem before, can anyone shed any light?

Thanks in advance,

Loops

Here you go mate
 
Hi all,

Just back from an EICR where one of the RCDS was testing out at 0.0ms for the 1/2, 1 and 5 tests both ways, not had this problem before, can anyone shed any light?

Thanks in advance,

Loops

Not had it for all 6 measurements, when I have had it on isolated occassions I have assumed the trip time was quicker than the tester could actually measure (I assume your using a Fluke)
 
It's a 30mA RCD tested using a Fluke 1651b which has no ramp test, tested using correct settings, wired up and isolated same results, was thinking duff RCD but wanted to check to see if this has happened to anyone before?
 
Apologies, it is a Contactum 63A 30mA DP RCD in a domestic property -

Associated standards:
BS EN 61008


Rated voltage:
220-250V



Rated current:
63A


Rated frequency:
50-60Hz


Switched poles :
2 pole


Minimum switch contact gap :
4 mm






Ambient operating temperature:
-5 to 40°C (24hour average not exceeding 25°C)


Maximum installation altitude :
2000m
 
So if it's type B have you got your tester set to DC. Has it got the type B symbol below.
 

Attachments

  • [ElectriciansForums.net] RCD 0.0s??
    image.jpg
    11.5 KB · Views: 86

Reply to RCD 0.0s?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
775
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
783

Similar threads

L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
650
J
The rcd spur being fitted is probably because there wasn't rcd protection of that supply.
Replies
5
Views
427

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top