Hi,

Ok so the new meter has been installed and the customer now wants 4 storage heaters, you can see the meter below.

Whats the best way to go about it as theres only one output.

He needs a new consumer unit anyway, do I just put it all in one CU or split it and have it in two CU's

But the timer issue, shall I use a contactor and a time clock inside a separate CU to feed the heaters?

[ElectriciansForums.net] Storage heaters
 
I would probably install one CU with a contactor and timeswitch installed in it, the contactor would switch the feed to the 4 MCBs for the storage heaters.
So for the layout of the board you would have a main switch, followed by your 24hr circuits, then a couple of spares then the contactor followed by the controlled circuits with the timeswitch at the end.

All in one box, nice and neat.

Also I would install a basic mechanical timeswitch rather than a fancy digital one, it's only got to switch on and off at the same time everyday.
 
Dave, I like your idea, I am planning on installing a 5+5 Hager board with Dual RCD, so Im just wondering about there being too much load on one RCD? I think theres two 3.5kW heaters and 2x 2kW, so 11kW in total probably.

Im just trying to visualise it in a board, maybe if I go for a large hager board, like one of those big ones, not sure of the model, ill get it all to fit.

So it will go

RCD ONE
MCB1
MCB2
MCB3
MCB4
MCB5

RCD TWO
MCB1
MCB2
MCB3
MCB4
MCB5

This is then the issue, do I put a third RCD in? its going to be too much with the rest on that RCD.

Perhaps just putting a smaller board in for them would be easier as I can use an RCD as main switch, then the MCB to fuse it down for the contactor wiring then then the time switch then the MCB's

what do you think?

Presumably I am switching the contactor with the time switch anyway, so its not like its going to switch 50A or something.
 
why not just install 2nd consumer -unit for s/htrs and apply for off peak metering...E7 / E10. Or am I missing something here?
Don't forget you have to inform Supplier /DNO that you intend to increase load.
no requirement for contacter etc
 
why not just install 2nd consumer -unit for s/htrs and apply for off peak metering...E7 / E10. Or am I missing something here?
Don't forget you have to inform Supplier /DNO that you intend to increase load.
no requirement for contacter etc

They have just had the meter changed for a dual rate one to supply E7 (see pic in OP), so they already have the metering in place. A contactor or other time-control is required as it is a dual rate meter.
 
Dave, I like your idea, I am planning on installing a 5+5 Hager board with Dual RCD, so Im just wondering about there being too much load on one RCD? I think theres two 3.5kW heaters and 2x 2kW, so 11kW in total probably.

The obvious answer to that is that teh RCD won't be overloaded if you choose the right size RCD ;)

Im just trying to visualise it in a board, maybe if I go for a large hager board, like one of those big ones, not sure of the model, ill get it all to fit.

So it will go

RCD ONE
MCB1
MCB2
MCB3
MCB4
MCB5

RCD TWO
MCB1
MCB2
MCB3
MCB4
MCB5

This is then the issue, do I put a third RCD in? its going to be too much with the rest on that RCD.

Perhaps just putting a smaller board in for them would be easier as I can use an RCD as main switch, then the MCB to fuse it down for the contactor wiring then then the time switch then the MCB's

what do you think?

Presumably I am switching the contactor with the time switch anyway, so its not like its going to switch 50A or something.

What is on the other 10 MCBs? don't forget diversity, the average house will rarely draw more than 20A plus the storage heaters should only be coming on when most other load is off.

I hadn't even consider a twin RCD board as I just don't fit them, I only use SPSN RCBO's. I guess it is personal choice and available space which decides whether you put it all in one board or two, but don't forget you will need one single main switch so may be an idea to feed the second board from the first.
Personally i'd look to get it all in one board as in my opinion it looks neater that way.

Have you considered the hot water in your designs? if they are having off peak heating they will benefit from a dual element hot water tank with on and off peak elements, or at least for the existing immersion heater to be used during the off-peak period but with the ability to be switched on at other times if required (a standard immersion heater timeswitch, nothing fancy)
 
That's not a dual tariff meter ? Why is it sealed as an extra wire has to come out of it ! !
Now it's sealed you can't do that

I cant see that another wire is going to come out of it looking at it on the photo he sent me, its 10 miles from my house so not particularly wanting to make another trip to look at it again.

The obvious answer to that is that teh RCD won't be overloaded if you choose the right size RCD ;)

What is on the other 10 MCBs? don't forget diversity, the average house will rarely draw more than 20A plus the storage heaters should only be coming on when most other load is off.

Personally i'd look to get it all in one board as in my opinion it looks neater that way.

Have you considered the hot water in your designs?

Very true, no they have a boiler, no immersion heater. The other MCB's yes half of them will be spare.

They have just had the meter changed for a dual rate one to supply E7 (see pic in OP), so they already have the metering in place. A contactor or other time-control is required as it is a dual rate meter.

Yes thats the plan...

why not just install 2nd consumer -unit for s/htrs and apply for off peak metering...E7 / E10. Or am I missing something here?
Don't forget you have to inform Supplier /DNO that you intend to increase load.
no requirement for contacter etc

They know, as they changed the meter for it, but not sure that its up to the easier option so will need to look at the options now to get it all in one board.

Has the client applied to have E7? I wouldn't fancy paying full rate every night to heat my house!

Yes its E7 or something for storage heaters, but i was hoping that it would have another wire out to be honest....
 

Reply to Storage heaters in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Pretty common for lights and sockets to get a Re-wire and the Eco7 circuits usually storage heaters /water heater to remain left as was. As for...
Replies
14
Views
2K
I am a landlord/owner of a flat. I am just about to spur off nearby sockets to provide the additional 24hr supply to new Dimplex Quantum storage...
Replies
0
Views
807

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top