Whats peoples thoughts on these pictures, 3P Db, Header trunking above, No leaks above, we believe condensation has built up on the face of the lid and tracked through into the gear tray, see the pic with the covers removed...............

[ElectriciansForums.net] Arc me up........................[ElectriciansForums.net] Arc me up........................[ElectriciansForums.net] Arc me up........................[ElectriciansForums.net] Arc me up........................
 
I wouldn't have said condensation alone would cause an arc like that. Especially in an LV board.
[ElectriciansForums.net] Arc me up........................[ElectriciansForums.net] Arc me up........................[ElectriciansForums.net] Arc me up........................

It was a very strange one to try and prove, at fist i thought maybe the caretaker having a fiddle with something he shouldnt but the flash marks are in the inside of the door proving it happened whilst closed,
 
I would have maybe said something loose inside the panel, finally moved due to vibration or similar. You'll struggle to melt copper like that without a direct short.
i thought that at first, when you look at the Mcb those prongs have a plastic cover over them and these were still in place apart from the centre cover had come loose after the fault along with the fact it being the second way down makes it even stranger.
 
Had a fault like that once, perplexing. Turned out to a split shroud on a SWA supplying an A/C unit outside on the roof, the water was getting in and making it's way down through the armoring and core gaps into the panel, Took some finding luckily I was called back to it when it was raining, worth a look. Good luck.
 
As all the burning appears to be down the middle was there anything that could of shorted between the front and the terminals?
Hi, there was nothing that could of shorted at all, clipped in nice and tight, only one of the covers had come loose and the others were still intact and secure, the busbars on the gear tray were still nice and clean
 
looks an expensive repair and once done it might just do it again
there is some rust showing on the cabinet

Yes it is in a hot plant room, there is some passive ventilation system which i dont really know much about, when we changed the DB we advised the client to check with the installer of the ventilation system, there is a large slatted grill in the plant room wall opposite this DB but about 4 metres away
 
What temp' is normal running ... does the room drop temp' fast when work shift has finished.... this is strong evidence of cold air condensation on the the warm mcb ... I get this often in old panels that run all day and at night the temp' drops like a stone, all the contactors etc get soaked in droplets ... once the arcing starts it creates a runaway reaction as it burns and changes to carbon the plastics etc which is a conductor ...which in turn allows more current ..etc etc etc ..


If your are adamant nothing has leaked down the back of the board through the busbar lines from an external source then condensation is your culprit.

Where is the air coming from that is venting through the room ...is it dried or straight from outside... if the later then a redesign of your ventilation as well as preventative measures for condensation need installing.

Ive had this issue many times under totally differing set up from a DC motor been cooled with external air which condensed in the steel venting and filled the motor up with water, to as mentioned before panels and DB's.

Ive seen paxolin shields and separators become conductors because of this effect Ill dig the pic up if I can.
 
Last edited by a moderator:
I would have maybe said something loose inside the panel, finally moved due to vibration or similar. You'll struggle to melt copper like that without a direct short.

Condensation can do this easily it carbonises the materials it tracks over and even deposits vapourised copper layer (check his pick of the rear of the cover).. once this happens the current increases and like mentioned in my previous post - it becomes a runaway effect until bang!!!!

This is from water ingress ..a drip in this case onto the busbar that ran across the paxolin to another busbar..the 2 bolts in pic 2 were bolted to adjacent phases hence the tracking from one to the other.

[ElectriciansForums.net] Arc me up........................[ElectriciansForums.net] Arc me up........................[ElectriciansForums.net] Arc me up........................

Note the repair was a temp' fix the whole lot has been upgraded since.
 
Last edited by a moderator:
Agreeing with all the above, it could well have started with moisture although the room doesn't look like it suffers from rampant condensation so I quite like the water-seeping-through-armoured theory. But something strikes me as odd, if it was caused by moisture. As in DW's pic, the insulation tracks and chars, self-heats and eventually starts a flashover, but by that time it's usually already black and crispy.

In your board, where the power arcing has occurred at the outer end of the busbar clips, the MCB case material is still very much intact. Most of the black deposits seem to be a result of the splash rather than charring of the plastic itself, i.e. there doesn't seem like enough damaged plastic to trigger a full-scale arc. I have to wonder whether there wasn't a wire trimming or something trapped behind the MCBs? Of course the arc might have started in the busbar pack and blown itself towards the outer ends of the clips but it still doesn't feel like the full story.
 
His second set of pics clearly show water has dripped down and caused rust, this is a newish clean install, if the air is been vented in from outside during the colder nights after a moist warm day you will be surprised how much condenses, like you say unless we are not privvy to some crucial info then I'll edge my bets its mostly occurred in spring with warm days and cold nights and again over the last week as night time temp's can be 10-15 degrees down on the day time and it drop very quick.

Where is this job is it in the sticks where air temps are getting close to frost over last week?
Any further info on the venting system too?

As for the SWA theory Nunes - they all come up-hill the conduit in the top is the only possible culprit but would be evident on the cables in it.
 

Reply to Arc me up........................ in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
720
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
543

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top