If I intall a 45 amp cooker isolator inside the kitchen cupboard can I come straight out of that and hhardwire into the cooker? So I dont have to install a cooker outletplate as there not.much room.behind.
Discuss hardwiring cooker straight into 45 amp isolator in the UK Electrical Forum area at ElectriciansForums.net
isolator feeding socket/+cooker point below satisfys everyone even the most ----I wouldn't install a cooker without an isolator, let alone direct from the MCB to the cooker!
yyes you can do it, but I would follow Rocks advice above this reply for the reasons he highlighted.If I intall a 45 amp cooker isolator inside the kitchen cupboard can I come straight out of that and hhardwire into the cooker? So I dont have to install a cooker outletplate as there not.much room.behind.
As far as I know there is no regulation saying you absolutely must fit a cooker outlet. It is more of a convenience thing for should you need to change the cooker. What kind of cooker is it? Is it a unit that fits in the kitchen units with a seperate gas hob? If so you'll probably find it comes with a plug top. Chop the plug off and fit an unswitched fused spur. Doesn't take up much room
yes we understand aron, however we have given you our advice mate and you will have to decide what to do, I think you have made your mind up anyhow by the look of your replies so we need not reply anymore with advice on this subject.I was going to hardwire the cooker into the isolator which will be in the cupboard and plug the hob into the isolator which has a socket on. I was not going to cut the plug of the hob. I was just going to make a hole for it.
yyes you can do it, but I would follow Rocks advice above this reply for the reasons he highlighted.
I wouldn't chop the plug off, manufacturers are tight as a submarines door! They'll do anything to void the warranty even for cutting the plug off!
Nonsense, that is an urban myth!
You are too wise, my friend!yyes you can do it, but I would follow Rocks advice above this reply for the reasons he highlighted.
Beat me to it!
I wouldn't install a cooker without an isolator, let alone direct from the MCB to the cooker!
i dont know the rating but the induction hob at home is on a 50amp breaker.If by cooker you mean oven, check the rating and if pre-flexed that your breaker is suitable - It's usually the hob (if electric) that pulls the most so that might want looking at - ask the guys here. In answer to your question, there's nothing 'wrong' with doing it as said above, just make sure it's suitable for the environment.
i dont know the rating but the induction hob at home is on a 50amp breaker.
there are plenty of 7kw induction hobs on the market (standard 4 spot hob)
Cheers Shanky for giving an example of what I was getting at, being that the cooker (oven I think) if pre-flexed might not be suitable to hard wire to isolator depending on breaker