A Short Guide to Working Out Cable Sizing | ElectriciansForums.net Est.2006 | Free Electrical Advice Forum
A Short Guide to Working Out Cable Sizing

A Short Guide to Working Out Cable Sizing 2016-08-22

No permission to download
It is the intention of this article to explain simply how to select the correct cross-sectional area of cables with particular single-phase loads in mind. I’ll refer to the tables in Appendix 4 of BS 7671, although these tables are reproduced in Appendix 6 of the IEE On Site Guide. We’ll assume that the overcurrent protective device will be providing fault current and overload current which is the normal situation.
  • Like
Reactions: Bender
Author
Sintra
Downloads
317
Views
2,958
First release
Last update
Rating
5.00 star(s) 1 ratings

More resources from Sintra

Latest reviews

Good

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top