    UK High Ze TNS - what to expect from DNO?

    Good thinking - the other side of that is my garage and also where the gas comes in so probably quite a tidy solution if it comes to it!
  2. S

    UK High Ze TNS - what to expect from DNO?

    Thanks UNG! I hadn't spotted that. The nice chap from SSE knocked on the door about 10 last night. He said he was able to get a reading of 0.7 ohms (just less than 0.8) but that it would probably be higher when everything was on. He said it probably still wanted doing. He said he'd log it and...
  3. S

    UK High Ze TNS - what to expect from DNO?

    Thank you! Yes I asked for the "better option" as we were replacing it, just wish this had been made clearer.
  4. PXL_20240828_184001588.jpg

    PXL_20240828_184001588.jpg

  5. S

    UK High Ze TNS - what to expect from DNO?

    Ah - the original report had all sorts of observations which led me to get the new consumer unit. This observation however was a "Further Investigation" and on the installation certificate it's now just a comment on the existing installation. Mostly just concerned with getting it put right -...
  6. Screenshot_20240828-191157.png

    Screenshot_20240828-191157.png

  7. Screenshot_20240828-190859~2.png

    Screenshot_20240828-190859~2.png

  8. S

    UK High Ze TNS - what to expect from DNO?

    Thanks - do you mean they should have notified the supplier themselves rather than leave it as a footnote in an installation certificate for me to find two years later? To be fair I see now it's also on the EICR that induced me to get the new CU so I probably could have been paying more...
  9. S

    UK High Ze TNS - what to expect from DNO?

    Here's the whole arrangement - supply helpfully hidden behind that gas meter!
  10. PXL_20240828_170739641.jpg

    PXL_20240828_170739641.jpg

  11. S

    UK High Ze TNS - what to expect from DNO?

    Clueless householder here! My wife told me John Lewis refused to plug in our new oven this morning due to "high readings on sockets". It looks on their paperwork like the "Pre Earth Loop Impedance Test" failed with 2.02 Ohms. I thought that was strange as we had a new consumer unit fitted and...
  12. PXL_20240828_155319945.jpg

    PXL_20240828_155319945.jpg

  13. PXL_20240828_155245997.jpg

    PXL_20240828_155245997.jpg

  14. PXL_20240828_130124726.jpg

    PXL_20240828_130124726.jpg

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks