  1. ImpededLoop

    Combining Two 12v DC PSU Outputs for 24v

    I'd buy a dedicated 24v psu. I can't see it working with the existing psu.
  2. ImpededLoop

    Hyundai dhy12500se Generator Issues with 1000w MH Lights

    I'd suspect its power factor thats the issue.
  3. ImpededLoop

    Combining Two 12v DC PSU Outputs for 24v

    I imagine that all the negatives are linked (and probably the positives too), so linking two outputs in series would just cause it to go pop.
  4. ImpededLoop

    fix the radio

    Got to agree its really annoying!
  5. ImpededLoop

    Electrical supply cable.

    Likely to be a paper insulated lead sheath cable. The outer jacket is a type of cloth which I think is soaked in bitumin. Used by the electrical supply authorities until the mid 1960's when pvc insulation took over.
  6. ImpededLoop

    No earth or neutral

    So you were getting 230V to neutral and cpc when they were disconnected, yet there's no fault?
  7. ImpededLoop

    No earth or neutral

    Probably a neutral - cpc fault on the cable causing an upfront RCD to operate. Someone has disconnected it to remove the fault. The outbuilding probably worked with the neutral and cpc disconnected due to the neutral current being diverted through extraneous metal parts in the outhouse. Was...
  8. ImpededLoop

    EICR - made me laugh

    Hard to tell now that the test results page has been removed. Makes a change to see the codings being on the more lenient side rather than dishing out C1's and C2's for non dangerous items.
  9. ImpededLoop

    Emergency Lighting contactor switch over

    You could, but why not just move the emergency circuit to the same circuit breaker as the local lights? You could put a test switch next to the dB.
  10. ImpededLoop

    Career paths

    It depends whether you want to stay on the tools or go desk based. If you want to stay on the tools, the inspection and testing C&G 2391is a good and well recognised qualification. If you fancy a more supervisory role, the design course might then be worth doing (used to be C&G 2396 or...
  11. ImpededLoop

    RCD protection for cables above a plasterboard ceiling

    It's 522.6.201 and 522.6.204 that give the answer. As I read it, it's either 50mm in, or an earthed metallic covering that is required.
  12. ImpededLoop

    Storage heaters

    The wiring diagram shows separate neutrals for each supply. You should be ok but phone the technical department if you're in doubt.
  13. ImpededLoop

    PSCC on 460V Split Phase Supply

    I'm pretty sure you should double the PSCC in this case. I was taught about split phase 180deg supplies, but I've never worked on an installation supplied with one.
  14. ImpededLoop

    Vaillant Ecotec 630 plus Wiring

    Have you got 230V at RT? Try removing the grey wire and link the RT terminals together. Has the boiler got gas? Is the system up to pressure? Is the boiler going through a venting cycle?
  15. ImpededLoop

    Obsolete Timeguard PIR

    Many thanks. I think this will be the only way to do it without rewiring the PIR's
  16. ImpededLoop

    Obsolete Timeguard PIR

    Many thanks for looking it up. Unfortunately the system that I was asked to repair is a two wire system.
  17. ImpededLoop

    Obsolete Timeguard PIR

    Can you still buy the PIRs though?
  18. ImpededLoop

    Obsolete Timeguard PIR

    The existing PIR cables are only two core, so probably not unfortunately.
  19. ImpededLoop

    Obsolete Timeguard PIR

    Cheers Tel. Voltek looks good, thanks. I couldn't find GED online though. EDIT: Just noticed the Voltek needs three wires. Unfortunately the existing installation only has two.
  20. ImpededLoop

    Obsolete Timeguard PIR

    A potential customer has an external light control system originally manufactured by Timeguard. There's a controller in the loft space which has a 2 core cable to each PIR which seems to be a bus wire. The PIR's are now failing, part number: SL099. I've found them on Google but they are...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top