  1. S

    CPC size of SWA Armouring

    Davesparks i was referring to table 54.7 of bs7671 which states if S>35 and the protective conductor is the same material as the line conductor this is S ÷ 2 S = 50mm 50 ÷ 2 = 25mm
  2. S

    CPC size of SWA Armouring

    Thanks guys appreciate the help, I'll double check the calcs tomorrow regarding disconnection time
  3. S

    CPC size of SWA Armouring

    Evening, Just joined upto this forum after a search online for some info, hopefully someone can help me? I have taken over a job from another contractor who has run in a 50mm 4 core swa from a substation to a TP&N DB roughly 100m away. My concern is that it appears they have not run a separate...
  4. S

    How big must the earth conductor be ???

    Evening, Just joined upto this forum after a search online for some info, hopefully someone can help me? I have taken over a job from another contractor who has run in a 50mm 4 core swa from a substation to a TP&N DB. My concern is that it appears they have not run a separate earth and are...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top