Search results

Search results

You will need 50 posts under your account before joining in with this thread because you can't link out without 50 posts first.

  1. M

    Megger MFT1730 software for Windows 10

    The software allows downloading of the stored test data to produce certificates. You can even 'blob' the individual results over to a cert as you test. The Onsite package has a full licensed version of the Powersuite software included with the tester
  2. M

    Megger MFT1730 Code LPE

    As the ramp test showed a result of 46mA with no trip would indicate an issue with that RCD especially as the other RCD in the board tested fine. Even a brand new boards can have faulty RCDs!
  3. M

    Megger MFT1730 Code LPE

    Did you try the ramp test on the offending RCD Would be interesting to see the result
  4. M

    Megger MFT1730 software for Windows 10

    Sorry to hear to you have not received a reply to your emails. Megger Powersuite has to be installed in Windows 10 Safe Mode.
  5. M

    Megger socket test lead

    Hi Simon, The mains test lead from the MFT1553 cannot beused for measuring R1+Rn but you can use the SIA10 mains test lead or a mainsadaptor as you mentioned.
  6. M

    Megger switched probe

    Hello brucelee The part number for the replacement tip set for the SPL1000 switched probe is 6121-562 These can be obtained via most electrical wholesalers and directly from our sales office (01304 502101) Kind Regards Megger Technical Support
  7. M

    megger 1552

    Hi iamelectric The voltage range on the MFT1552 has a minimum resolution of 1 volt and allowing for accuracy figures it is perfectly acceptable for the unit to display 1V Kind Regards Megger Technical Support
  8. M

    Megger 1553 error, what's the problem?

    Hi VoltzElectrical Sometime during the no trip loop test the MFT1553 may come up with an error that seems to indicate ERP or ErR. Generally the error is trP which indicates either a momentary disconnection of the earth testlead or an intermittent cpc during the no trip test. The tester simply...
  9. M

    megger 1552

    Hi iamelectric Rechargeable batteries are capable of fairly high short circuit current and the MFT1552 does not have battery protection So it possible failure in the instrument power supply may give rise to a high current flowing that may further damage the tester. Kind Regards Megger Technical...
  10. M

    Megger earth & loop impedance testing event.

    Re: Megger earth & loop impedance testing event. Hi, just to let you know these events will be held all over the UK, but we have only just started organising them and some of our regional sales managers have obviously got sorted out sooner than others. Please keep an eye on this link to...
  11. M

    err 79 on megger 1552

    Hello crow11 Error 79 on the MFT1500 Series stands for ' invalid parameter in result display routine ' which in simply terms is electric noise or harmonics on the circuit under test. This noise may come from computers, high frequency lighting or downlighter dimmable 'transformers'. In addition...
  12. M

    Megger switched probe

    Hello luke12345 The alternative probe for the MFT1552 is the SP1 Part number 6220-606 Kind Regards Megger Technical Support
  13. M

    Megger MFT1553 problem!!

    Hello rusty196500 Error 70 on an MFT1552 indicates an internal reference voltage is out of limits. Please check the batteries; if the problem persists then a service is the only option. Our service department can be contacted on 01304 502243 Kind Regards Megger Technical Support
  14. M

    Difference Megger 1730 and 1835

    Hello Northring The difference between the MFT1700 and MFT1800 models is not just a firmware change. The printed circuit assemblies, in each Series, are completely different due to the different function requirements between the UK and the continent. Regarding firmware updates; Megger, like...
  15. M

    Megger 1720, rechargeable or not, that is the question??

    Hello mickytuff When switching between the different type of batteries have you selected 1.2V or 1.5V for rechargeable or alkaline respectively in the setup (spanner mode) on the MFT1720 tester? The correct voltage should be selected to ensure efficient use of batteries. Regards Megger...
  16. M

    NICEIC Certification Scheme Megger powersuite profesional NICEIC templates

    Hello Mr Yeates As you purchased the software after July 2011 you are eligible for a free of charge update for the NICEIC certs for Powersuite. Please contact our software support desk on 01304 502102 for details Kind Regards Megger Technical Support
  17. M

    Megger 1552 vs 1720

    Hi bobby101 As MarkieSparkie has already mentioned, the basic accuracy for both MFT1500 and MFT1700 Series testers is ± 5% so that different testers can give readings that differ by 10%, well within the EN 61557-3 standard. Based upon this information, for example, you may have 4 MFT testers, 3...
  18. M

    Megger Powersuite

    Hello Darryl If you send an email and your phone number to [email protected] we will contact you and provide detailed pairing / comms number information. Kind Regards Megger Technical Support
  19. M

    Megger BM203 bin or repair

    Hello UKMeterman Unfortunately the Megger BM200 Series are no longer supported with no spare parts available. There are still spares available for a few BM Series instruments. Kind Regards Megger Technicial Support
  20. M

    Megger MFT 1552 battery life and level

    Hello Busy Bee Some MFT1552 testers display the battery voltage by switching the tester to the off position and pressing the yellow 'TEST' and red 'LOCK' buttons together, while the remaining testers briefly indicate the battery voltage when the unit the tester is first switched on. (V3.5 is...