  1. W

    3kw heaters installation

    Thanks for the advice and thoughts guys. I’m thinking to go with 5x radials. There is a new dB going in at some point soon so capacity is good. I will look at location of solenoid/ control box as the majority is open plan so noise of a clunk would be an issue. Cheers Much appreciated ?
  2. W

    3kw heaters installation

    Hi, I’ve been asked to install 5x 3kw ceiling heaters in a room for a salon. I just want to check how you would install them? I’m thinking a radial in 4mm2 cable (singles in conduit), from cu to thermostat, to contactor to heaters, 13amp f/spur at each heater? Customer wants them all to come on...
  3. W

    More than 1 circuit on mcb

    Yeh 5 final circuits in 1x 6amp mcb. Looks like they have just added to the installation over the years, but instead of upgrading board for more ways, they have just put them all in 1.
  4. W

    More than 1 circuit on mcb

    Hi, recently carried out an eicr at a rented property. There were 5x 1mm in a 6amp mcb for lighting.. my question is what code should I be looking at for this?? I am sure I have heard someone mention or read somewhere about overpopulating an mcb should be a code 2... but then i have also heard...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top