yes right next to it, why?
1588271646
hi dave , I am not sure i follow what you mean here. surely if anything is reversed upstream (so to speak) the end appliances that rely on phase rotations for their direction (3 phases motors in this case) will be running in the opposite direction . Unless...
thanks dave ,I will do but the only potential problem that I see with that is that the customer will inccur more down time for his premises and the rotation of all the 3 phases motor will need to be reversed .
yes sequence, but I tested it with my trusted phase rotation unit and found the sequence at origin to be anticlockwise . Now I do not know if DNO is required to provide a clockwise phase sequence or not .
Hi all,
What are your views on phase rotation.
Whilst doing an eicr for a customer's premises I found that the phase rotation at the origin was anti clockwise .
the eicr form is asking for verification of phase sequences , which there is although anticlockwise .
What would you do there in the...
Hi everyone,
I have been asked by a customer to resurrect some of their very old testing equipment .
Long story short , I have managed to get an old Ferranti HV insulation tester back up and running but , I know for a fact that the next thing he is going to ask me is , "can someone calibrate it...
As mentioned in previous posts , the motor windings must be tested so see if there is any damages to the insulation . You ll need an insulation tester and carry the test at 500v .If you do not have the equipment nor knowledge I suggest you pass this on to an electrician .
It looks to me that the capacitor has been used to create a 2nd phase with a delay of 90degrees I have seen in the past a few times . If faced with this problem I would typically suggest to the customer to replace the capacitor setup with a Variable speed drive with a single phase input and 3...
There is only one cu in property.
The D is in bracket as quoted in report .
As for being incompetent and steering clear of Eicr , on the report he is described as a qualified supervisor and judging by the name of the company it seems to be specialised in inspection and testing , so I am not...
Thanks guys, that's what I was thinking .I just wanted to be sure . I will try to upload a picture of the cu later on .
I just wonder if the spark needs to go specsaver and confused the B with a D on the Mcbs marking.
Hello everyone,
I was wake by a friend to have a look at an Eicr that was done on his rental property .
The Eicr says I quote :
"Due to the c2 codes listed in section k , this report is unsatisfactory. The old consumer unit has type 4 (D) breakers where make it impossible to achieve test...
Hello everyone.
I am originally maintenance electrician who decided to work for myself about 6 months ago after getting fed up of working for others.
I started my apprentiship in 1994 in France in a company building special purpose machinery for industrial joineries and the automotive industry...
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc