Thank you replying. The way I see it is that there are two formula at play here. The recognised formula for resistors in parallel (1/R=1/R1 + 1/R2) and the derived formula for RFCs (R=(r1+r2)/4). Using your own example of 0.3 r1 and 0.5 r2, the recognised formula gives R as 0.225 ohms and the...
Thank you all for taking the time to respond. "happysteve" in post 23 is agreeing with my original post.....ie the formula does through up discrepancies/variations if the live conductors and cpc are of different csa (as his graph clearly shows)
Hi, I'm not an electrician but a keen amateur. I understand the testing on RFC and how it's done but couldn't get my head round the (r1+r2)/4 calculation. I've trawled this site (and others) and it seems to me that a lot of people struggle to explain this fully. The truth is that this...
Kuffs.....I like what you say as far as letting people know you are not a qualified sparky. I'm not qualified but have worked as a mate since I retired and have always been interested in domestic stuff. In my experience in the forum, if you are honest and know your limitations you won't get...
Kuffs.....I like what you say as far as letting people know you are not a qualified sparky. I'm not qualified but have worked as a mate since I retired and have always been interested in domestic stuff. In my experience in the forum, if you are honest and know your limitations you won't get...
Thank you all for your replies, you pointed me in the right direction and I found this....
"The maximum value is R = 50/Ia. Where Ia is the operating current for the protective device in 5 seconds. Ref. 413 - 02 -28. GN3 recommends less than 0.05 ohms."..
.
...it might not be bang up to date...
As can be seen from my profile I am not a qualified electrician but I'm studying in my own time just for the sake of it. I understand the principals of earthing and bonding but in this video by GSH Electrical....
.....at 2:10 minutes in he says exposed conductive parts under earth fault...
Thank you all for taking the time to reply. I've watched almost all of John Ward's videos (on this and other subjects). After reading all your replies and revisiting his videos I think I'm nearer to understanding what's going on. On the "unearthed" secondary winding, rather than thinking of L...
As can be seen from my profile I am not a qualified electrician but I'm studying in my own time just for the sake of it. Everywhere I look for info on isolating transformers I get something like this "This means that the isolation transformer secondary side must not be grounded. It would create...