    Bonding 10mm oil pipes

    Sorry,both test with main earth disconnected
  2. D

    Bonding 10mm oil pipes

    Hi Izzy I did do a test before I bonded the pipes to the MET,water was 0.07 or so,oil pipe was0.21. after bonding to met,both measured 0.01
  3. D

    Bonding 10mm oil pipes

    Hi chaps Done the job today,a 951 was ok,I got the external blue type,and it worked a treat,took it easy tightening it though. test all pipes and good continuity,below 0.01 ohms. happy days
  4. D

    Bonding 10mm oil pipes

    I know the feed to the aga definitely needs bonding as I've tested that and got a reading of 0.01 ohms,the other two feeds might be sleeved so your right they might not need to be bonded. my only concern is if the sleeping breaks down over time. thanks for the advice guys.
  5. D

    Bonding 10mm oil pipes

    Cheers chaps, I think the 951 only goes down to 12mm though
  6. D

    Bonding 10mm oil pipes

    Cheers for that. I did have a feeling it was the same reg for an oil pipe,the two supplies from two different tanks threw me,any ideas for a bonding strap that would fit that size of pipe (10mm) ?
  7. D

    Bonding 10mm oil pipes

    It's the fuel for the boiler instead of gas,so a 10 mm main bond is required as you would do for a gas pipe.
  8. D

    Bonding 10mm oil pipes

    Hi Never had this situation before,I'm changing a csu in a property,TT,no probs. The main house has a 10mm oil pipe feeding an AGA and a boiler ( I can only gain access to the aga pipe),this is being fed from one oil tank,the second oil tank feeds another boiler at the other end of the house...
  9. D

    Bonding main water PVC

    Cheers all,so as SS says if I test from MET to pipe work and reading is above 22.5k ohms I don't have to bond,does it make any difference that's it's a TT system? I haven't got GN8 will have to invest in a copy.
  10. D

    Bonding main water PVC

    Cheers all,so as SS says if i test from met to pipe work and the reading is above 22.5 k ohms I'm ok, I havnt got gn8 will have to invest in a copy. I presume it makes no difference if it's a TT system.
  11. D

    Bonding main water PVC

    Hi all, In a bit of a quandary,main water incomer is PVC ,from stop cock in property all copper. Now,do I bond the copper or not,read OSS and it only says recommends bonding to copper,I've been on other forums and had mixed replys,50% say yes,50% say no. Any thoughts?
  12. D

    changeing csu

    Cheers all, I think I'll go with the rcbo route,bit more expensive but more practical, ie nuisance tripping !and its only 3 circuits.
  13. D

    changeing csu

    Hi all Changeing an old wylex csu that has 3 16A storeage heater circiuts on it(TN-C-S). Can the new csu be a normal one or does it have to have rcd protection? Cheers
  14. D

    tt systems

    Hi all,just started using this forum,amazed theres so many people on it. I have to change a board on a TT system(haven't done one before). The cpc looks to be around 6mm(not sure untill i test it wether to change it to a 16mm),and has an old rccb protecting a wylex db. Can I use a 17th dual...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top