Ok, say you've got a lighting run with the last fixture being 1,280 meters away. 1,800 watts per phase 3 phase, 277/480Y volts though in this example we can use 230/400Y for the ease of discussion.
My question is- what size wire do I run for each phase and earth? What disconnection time do I...
There is no cost benefit. They are just an empty fire extinguisher. EFLI and plug fuses provide 100% parallel and earth arc fault coverage. That leaves serial events, where arcing is the end stage of joule heating assuming combustion has not already started. 90% of all electrical fires start...
My understanding is that in India, all final circuits are required to disconnect in 0.4 seconds or less. Personally I like the idea.
An exception for 5 seconds is needed for sub circuits though- 60 amp life safety feeder must selectively coordinate with the final OCPDs.