Alright.
So double checking that would mean a hard wired cooker could get away with 5 seconds, but a flex cooker would require 0.4 seconds? In the US almost all cookers have plugs on them.
Does anyone know why the 0.8 and 0.4 second disconnection time requirements are now extended from 32 amp circuits to 63 amp receptacle circuits? Is this because the supply sources are getting stronger?
So basically TN vs IT? I can't picture at 133/230Y TN system needing the same disconection time as 230 volt IT. Both are none distributed neutral systems.
Julie, mind blown! I had not realized the difference, now I see it.
Can I ask- why does having the neutral distributed make a difference?What is the theory behind that?
What is the max disconnection time for an IT system? I think it would be shorter in that an MCB would only be triggered after a fault on two individual circuits hence double the loop impedance?
Sadly nothing, however I've personally encountered this before (red color) and it was indeed copper all the way through.
For some reason now and then US rolls of NM end up with odd color copper on one of the conductors.