My understanding is that I cannot use 1-208.b for a chicken coop because it is housing livestock. For any other type of building my understanding is that either 10-208.a or 10-208.b can be used for the grounding conductor
Isn't it exactly what 10-208.a says?
Thank you. In my summarized code book based on CEC 24th edition it says:
What is the other 7 feet rule? Note that my question was regarding protection of the cable within the garage. In the coop the cables will be protected everywhere.
Hmm, this also seems to differ from the information I...
Thank you! There will be a ~1000 W water barrel heater to prevent water from freezing in winter and a water pump to circulate their water. I want to keep an option to have heating lamps. There will be some LED lights. I also need electricity for some actuators (automated door, ventilation...
Hi,
I want to bring 2 x 20A (@120V) to a chicken coop. It will be powered from my garage panel which will require 140' of cable. 85' in the garage along 2 walls, and 55' buried between the garage and the coop. I used a few voltage drop calculators and it looks like I will need a 6/3 to stay...