Well I calculate both for obvious reasons but have been calculating them both in the same way and ending at the voltage and not calculating the percentage.
For example (mVAm x L x Ib) ÷ 1000 = X volts
Then as long as its been below 11.5V, all OK
But now figured that 11.5V as a percentage of...
Think I may have been oversizing cables for some three phase circuits...
For example, when ive calculated a 11.5V volt drop on a general circuit I've took this as being the 5% allowed but I've just come to realise that maybes this is actually a 2.875% volt drop at 400V
Can someone confirm...
Looking to purchase one of the above.
Preferably an electric torque if there's such a thing? One I found on the Web said it only tightened to 0.2nM and then had to be manually tightened after that.
Any recommendations?
Thanks.
Just curious as to when people are calculating volt drop, how close you allow your calculations to get to the 3% and 5% values before you decide to up the cable size?
For example, if your calculations brought you to 11V for a general circuit would you be OK with that?
Can anyone advise when SPDs are required to be installed on commercial properties?
I'll always install them on a full rewire of a commercial property or if I need to install a new DB, I'll make sure to fit one with an SPD installed.
What about if its a large store, 36 to 72 way existing board...
I'll have to check regarding the overload relay but thinking about it I'd imagine there is, yes.
I'd still have thought the smaller the fuse size, the safer it would be though. Obviously ensuring its not too small that it would be tripping for no reason.
I was thinking more for overload protection. If the motor is only supposed to be running at 12.3A, surely letting it continuously run at say 25-30A as a 32A breaker would can't be good for it?
So in this case, the manufacturer has recommend "fuse rating 32A". Would you personally still fit a C32 as they've recommended 32amps or would you ever be tempted to downgrade the fuse rating knowing a C-curve will stop tripping on start?
Thanks for the info.
I figured a C32 would be too big and a C16 would be better considering the normal running current of 12.1A and a C16 would cope with the 65A start-up current due to the 5-10x tripping characteristics
A cellar cooling system with the main supply going to the indoor unit.
Spec sheet gives the following figures...
12.1amps FLA
65amps LRA
32amp fuse recommended
My question:
Why a 32amp fuse? Have they based this on HRC fuses perhaps and not advised that?
Wouldnt a C-curve 16amp 60898 be...
Is that correct? I've done some research and never heard anyone mention that yet?
If so, that means there was never an issue to start with which is the best result.
Hello to all,
Rather than start another eddy current thread, thought I'd just tag onto this one.
Cables contained in metal trunking which is bushed to the side of a 12TP dis board. Lives and neutrals go through one 50mm brass Bush into RCBOs. The earths go through another 50mm hole which is in...
Ive never seen them put into practice so wasn't sure how sensitive they are. I was just thinking it would make things a lot cheaper until the prices came down. Much like when dual split boards were much cheaper than full RCBO boards but now the prices have dropped.