  1. S

    Diagnosing tripping RCD from septic tank pump

    Yes they were still connected at the CU if it was N/E fault I would have never been able to reset the RCD even with the MCB flipped? Anyway, I severed the cable just before it went underground and now the fault has gone so it must be the underground cable. I have purchased some wiska boxes, SWA...
  2. S

    Diagnosing tripping RCD from septic tank pump

    Ah yes thats a much neater solution with the the SWA glands, thanks a lot for the info. Now to cut this wire see if it makes a difference other wise I guess I'm running a new wire from the consumer unit which would be quicker and easier than trying to diagnose the whole wire as it's quite a long...
  3. S

    Diagnosing tripping RCD from septic tank pump

    It's definitely not the pump as you say, I have a put a plain old plug on the end of it and currently have it running off an extension reel just fine. I have traced the cable through the house and it looks fine, it's currently one long piece. My plan was to cut it just before it goes underground...
  4. S

    Diagnosing tripping RCD from septic tank pump

    Hi all, Quick question I have a bio tank pump that had been working fine up until today, it tripped the main rcd out. If i isolate the bio tank as it has its own radial I can reset the RCD. I disconnected the pump and still the same I disconnected the industrial connector and had the bare wires...
  5. S

    UK Adding RCD spur doesn't set but consumer RCD is fine

    I thought I had I have deffo tested them in the house, I have one of those cheap RCD socket tester things that tell you if your feeds are reversed and let you test the RCD etc but I can't find it...typical. I will make sure I dig it out and test again.
  6. S

    UK Adding RCD spur doesn't set but consumer RCD is fine

    Thanks for all the input guys the garage is where the electricity comes in the meter(s) are there. I have attached a picture, the house has its own separate consumer units. The gate is attached as a spur off the garage sockets. No matter where I put the RCD in the garage it doesn't set, i think...
  7. S

    UK Adding RCD spur doesn't set but consumer RCD is fine

    I thought I read somewhere it was best practice for cables that went external, also I was planning to maybe add an exterior socket also which again I thought was best practice. Still it makes me think there is something wrong with the main rcd. I didn't mention this is from the garage where the...
  8. S

    UK Adding RCD spur doesn't set but consumer RCD is fine

    Hi all, I have ran added a fused RCD spur off a socket to feed some electric gates. I figured as it was going outside I would put an RCD on the spur on it as I had one kicking around I believe it's probably unnecessary but when I connect it to the supply it will never set and constantly trips...