  1. MJPD29

    Extending tails - SWA or Hi Tuff ?

    I would use swa, especially if any part of the route could require rcd protection with hi tuff.
  2. MJPD29

    Sanity check on plan for CU replacement (MCB to RCBO AFDD)

    The price of this to buy without labour is going to be eye watering. There is currently no requirement to have afdd protection for circuits in your house, it is only a recommendation for socket circuits, but not mandatory.
  3. MJPD29

    UK Is an SPD required for a loft conversion?

    I’ve never seen one activated. After some sites I’ve seen recently that have suffered from lighting strikes I’m starting to wonder how useful some of them are.
  4. MJPD29

    Electricians on building sites. What is is really like?

    It won’t happen there are a lot of people with very little or basic skill hiding on building sites bending conduit with no idea of how to do anything else. It’s the fear of the unknown, most of us have it but an easy maintenance job certainly sounds preferable
  5. MJPD29

    Electricians on building sites. What is is really like?

    8-4.30, cold in winter, full of some of the best characters and biggest morons I’ve ever ever met. People rarely get kicked off site as in my experience they are generally so many people stealing a living that kicking them off could leave the site with no staff. Thoroughly enjoyed site work...
  6. MJPD29

    UK Is an SPD required for a loft conversion?

    Out of interest, has anyone ever had to replaced an spd because of a surge or seen one that’s done its job?
  7. MJPD29

    UK Solar SWA cable run 10mm or 16mm

    Answering questions at 4.01am?? That’s dedication
  8. MJPD29

    Dodgy trade pictures for your amusement! - 1 Million Views!

    How do they sleep at night? That would drive me mental
  9. MJPD29

    Ethernet and Power cable to be run underground

    Why say that? Both insulation rated to the highest voltage present
  10. MJPD29

    Ethernet and Power cable to be run underground

    Swa power and swa data alongside each other, no issues.
  11. MJPD29

    Ev charger rccb fault

    Sounds like they aren’t up to the task, although from the cable sizing id guess these are pretty small chargers. What size are they?
  12. MJPD29

    Rats and tripping MCB

    I’m confused, when you say IR on line do you mean IR line to neutral or line to earth? 3Mohms wouldn’t be enough to trip an mcb.
  13. MJPD29

    Rats and tripping MCB

    L-N shirt would trip mcb, not rcd. MCBs are for overload AND short circuit protection…
  14. MJPD29

    Borrowed neutral on split load board

    Have you tested the current earth leakage and/or ramp tested the rcd?
  15. MJPD29

    Solutions for LED inrush current

    You’ll need to check you can still meet zs requirements for ads when changing from a b type to c type.
  16. MJPD29

    Borrowed neutral on split load board

    Have you got an earth leakage tester? You could clamp it and see what leakage is at any given time and ramp test the rcd to see what it is actually tripping at. You could find that it’s close to its limit and turning on a light in that lighting circuit is pushing it over the edge.
  17. MJPD29

    NVQ 2357-99, Job write ups

    It’s not really. Just write about what you’re doing in the pictures and how you do it. Include all details with glands etc, it’s basically just talking about what you do on a daily basis. Don’t panic, it’s actually very simple.
  18. MJPD29

    electrical condition report

    Some of the points should have been picked up by previous people doing the testing. Sounds like this is a thorough report. Not everything is mandatory to be done, but plenty of it is.
  19. MJPD29

    IET BS7671 Electronic Copy required

    If your going to be trading as a company doing any sort of electrical work you really should have your own copy.
  20. MJPD29

    Electrician to connect tails after isolator fitted (EDF)

    Always worth remembering that meter fitters are untrained and have almost zero electrical knowledge. They go by what their job sheet and tick box exercise says, connecting a cable could cause a blind panic and lead to 6 months off with stress for them.