    Bonding to gas and 544.1.2

    So, where is that from?
  2. N

    Bonding to gas and 544.1.2

    If you want to comply with BS 7671 then that states that it must be after entry to the premises, or words to that effect. If you put it outside then it is a deviation that must be noted. Then, if you bond outside, you must defer to gas regulations as to how you bring the cable into the premises...
  3. N

    Bonding to gas and 544.1.2

    Bond is to be inside the premises, some of the gas industry paperwork is simply wrong. It is doubtful that the gas fitter knows what is required. He's certainly NOT a registered Engineer, that's for sure.
  4. N

    GEFRAN 40B96 - Pressure Imdicator

    It always puzzles me why machine builders put devices on their machines that are not needed. If they didn't fit them they could save themselves loads of money, and either keep that as profit, or sell their machines cheaper and sell more of them, possibly even cheaper than their competition who...
  5. N

    Demonstration of an AFDD by wylex

    AFDD's are coming in to try and eliminate the absolutely rubbish domestic appliances that are being sold, which are barely compliant if compliant. The trouble is the appliance manufacturers are too powerful to tackle, and the fault is being placed on the electrical industry, not the appliance...
  6. N

    Contactor control advise

    I hope that you are following best practice and getting the 13849-2 validation done by a 3rd party DW? :joycat:
  7. N

    Contactor control advise

    Just be careful as you are designing a safety system now which is outside the remit of BS 7671, and the consequences of failure could be considerable. Make sure you are insured to do this, and make sure that the contactor whilst 100A rated has a suitable characteristic for the load. Darkwood is...
  8. N

    Anyone go the BBB to hand - reg regarding mix and match

    So, where does the Electrical Equipment Safety Regulations come in? This is the UK implementation of the Low Voltage Directive. Ok, technically you don’t have to type test, but, then, as the manufacturer of the assembly, you have to complete your technical file, proving that the equipment you...
  9. N

    Installation regs on multiple earth rods.

    BS 7671 defers to BS 7430 on the detailed information and specifics of earthing, and there is a bit to it, but, to avoid interference rods should really be twice the driven depth apart.
  10. N

    Anyone go the BBB to hand - reg regarding mix and match

    All the new regulation does is bring this into BS 7671 because the requirement in law was being ignored by sparks. The legal requirement for type tested assemblies has been in place since 1994, so it's not new, it's just been ignored by electricians for the last 24 years and the "industry" is...
  11. N

    Anyone got a small van for sale?

    Apparently they can!
  12. N

    NICEIC Certification Scheme What happens on a NICEIC assessment

    Is this the guy that removes DNO fuses for isolation regardless of the rules?
  13. N

    New sub board for shed swa advice.

    There is not necessarily a problem with exporting an earth if it's done correctly. I think that there is some misunderstanding with regard to this, and yes there is a lot of guidance on doing this. I think that the discussions with regard to the exporting earths has been quite vociferous and...
  14. N

    New sub board for shed swa advice.

    It should only be an issue with open circuit PEN/CNE conductors, but even on presented TN-S supplies these days they are often TN-C-S further upstream. They annoying thing is the extents that the paying customer (& thus the spark) has to potentially go to so that the DNO's can get away with a...
  15. N

    New sub board for shed swa advice.

    That is pretty much correct spin. Under rule 43, the coroner wrote to theNICEIC, and they wrote to all their QS's & PDH's at that point in time. Or at least they told the Coroner they did, because if they hadn't the Coroners powers could have taken that further.
  16. N

    New sub board for shed swa advice.

    I dunno, but that was the expert witness evidence provided by the forensic investigation. If the circuit was repeatedly energised then it may well have blown the cpc away, we don't have adequate detail to know. What was the fault current, I think it may have been a block of flats? As she was...
  17. N

    18th.Edition 411.3. 1.2 Doubts in my mind !

    gerry, Not you, I'll say before anyone jumps on me, but, there are dim-wit's out there. It is not uncommon to see plastic pipework with a copper section fitted about 6" long with a bonding clamp fitted to it. Quite what that accomplishes apart from bonding the 6" of copper I don't know. The...
  18. N

    New sub board for shed swa advice.

    If you read the Coroners report and the expert witness investigations, the cpc was vaporised by the fault, I'm not saying that there was no dead testing, but it would seem that the cpc had been vaporised before the insulation resistance testing had been done, i.e. the installation was energised...
  19. N

    New sub board for shed swa advice.

    No worries, sorry Ian, I think that there is merit in discussing exporting earths, just not in this thread. I think he has some valid points, but may not have made them well. #e5 has been in my signature on here for several months now, perhaps even a year, or more.
  20. N

    New sub board for shed swa advice.

    No longer as it is not the same as the outline of the TFL badge any longer.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top