Make sure the zone is set to entry exit,you might have it set to Immediate,on some panels it might be only 1 zone can be entry exit,also you may be walking though another immediate zone without it set to walkthough
That switch would be hard to wire as it switches different contacts with no common, you also need to make sure they are break before make switches,as well as suitable for the loads involved
I can't see you ever getting a low enough Ra or ZE to meet disconnection times on a fuse or mcb, have you asked if they will pme the supply?
A line to earth fault in the swa may never clear in any time.
An electrician installed a NEMA 6-20 20A 230V outlet in a surface box for me in my garage, on a dedicated 20A breaker. He was even kind enough to follow code and run a neutral wire:
I would like to replace this outlet with a side-by-side single 6-20 and 5-15 duplex so the box can be used for...
thanks for the confirmation this is what i thought.
i cant think of what use this device is .
i have seen David Saverys Arc Fault Detection Device testing videos most interesting
we have had installed some Hagar ARM932U Arc Fault Detection Device in one of our care homes.
they had reported tripping issues , so i tried to do an (RCD) Residual Current Device test.
it wont trip at any current.
looking it up it seems they are not also an rcbo . if so whats the point of them...
if you use the 6mm2 version of the wagos and its in a MF box ,suitably located ,it should be ok.
The only concern is the protective device ,protecting the flex cable,this is no different to a flex outlet
I was more thinking why a C curve breaker , a 32 is most likely needed in case all get put on together, but the motor is probably not much of the load ,so i would guess not too much inrush current to require a C device, you could measure with a clamp meter with a max functon to test this
I would be asking why it's on a C32,while it is permitted I don't think it's a great design to exceed maximum ZS and rely only on the (RCD) Residual Current Device partof the rcbo
neutral and earth are already connected upsteam (at least in england anyway and i imagine else where as well).i cant think of any upstream fault that would affect an (RCD) Residual Current Device .
a downstream neutral to cpc fault will only trip an (RCD) Residual Current Device if a circuit...
Niceic dont allow 3rd party QS sign offs, the main problem i found was building control notifications ,we actually paid the local authority the first time !
Otherwise you can just use there green certs.
Or just use the bs7671 templates