I thought any conductive material in a moving magnetic field will induce a voltage.
Magnetic flux is a thing but it's the moving flux or conductor moving though a magnetic field that induces a voltage.
I was also taught that below 100 amp current is unlikely to be a concern.
Having said that I...
1. interconnected circuits would be a C2 mainly as there is not a direct connection ,so some type of fault ,21 ohms sounds like a circuit or load,
about 11 amps could flow though that.
2. operational limitation or come back after midnight (dead test only otherwise)
3.its a sub main after an 80...
I hope it is scrapped what a waste of time (pun intended) , figuring out what timers/clocks need adjusting ,the only benefit I ever got from it was an extra hour in the nightclub
You can get a usb dvd/cd player for less than £20 or you can go here and download the update Download software updates - https://www.fluke.com/en-gb/support/software-downloads
At 240 volts a 10v drop won't be much of an issue at 24v it's a big deal,you would have to work out the minimum accepted voltage at full current and use ohms law to work out the best size of cable
after changing a consumer unit I have a high level flood light and photocell that can’t be reached.
on the EICR I can LIM these due to height .
the photocell is a NEMA plastic double insulated type
the floodlight however is a SON-T and I suspect its a metal case !
I would C2 this, cable is not suitable for the environment its installed in, we would C2 a socket for equipment likely to be used outside , cable is not buried at a sufficient depth to avoid damage.does the cable contain carbon black to prevent UV damage ?,maybe even cable not supported correctly .
I think over there you would call it a gfci which we call an (RCD) Residual Current Device or RCCB, an RCBO here is an (RCD) Residual Current Device with an mcb in one unit
Seems to be picky about the wrong things, I'm sure there is no reg that mandates ordered terminals,but as above many of the others are C2 in my opinion,the C2 for fire rated lights is probably not either
Not many people could feel 24 volts,check the obvious like no stray wires touching the casing,if you have a meter check ac and dc voltage between case and a true earth
What voltage is the transformer? If you are getting a perceived electric shock there must be a power supply fault if its extra low voltage,earthing the case may help or it may just finish off the power supply,.
I have changed the supply to a 16 amp mcb , my ZS at the bin store light is 1.29 ohms ,fault current of 186 amps.
my read of the time current curves is that the local 6 amp will trip possibly the 16 amp as well ,so I may not have achieved much at all!