It's coming out anyway so it's a rhetorical question.
What do you you all think of this?
Bits of wire used to bridge the bus bars and don't single phase consumer units need a linked switched line and neutral?
Just to notify all those who have not been informed about the Corrigendum to BS_7671:2018+A2:2022 ,This will be published on may 15th 2023.
it seems safety services in 443.4.1 is redefined with some examples removed !
701.1 no longer references birthing pools.
i expect we will find out more...
In short the (RCD) Residual Current Device must be protected by a suitable overcurrent device. BEAMA issued a technical bulletin about this:
https://www.beama.org.uk/static/uploaded/6861a2e1-d8d4-4d81-b5fa710ba60ca4a7.pdf
Its in all of the higher risk residential building
421.1.7
Arc fault detection devices conforming to EN62606 shall be provided for single phase AC final circuits supplying socket outlets with rated current not exceeding 32A in:
• Higher risk residential buildings
• Houses of multiple occupancy...
Some updates, I have secured the DNO earth and clipped the tails.
I did wonder how common it is for a dno to supply an earth from an overhead pole supply
In any case it wont be for fault protection unless its TT earthing.
over 200 ohms Ra is considered unstable .
Your better off conducting R1+R2 and comparing these to the maximum ZS (roughly) , this will also ensure that it disconnects during a line-neutral short circuit.
Thanks for that , im just about to clip the tails to stop movement, i take it when our so called building works have finished I can use the supplied earth?
will the spd work with only 16 amp earth fault current at 230 volts anyway.
or maybe it will work better at clamping a surge ?
I have added a consumer unit and an earth stake to this so called temporary supply.
This is a full rcbo board apart from the mcb to the spd.
Would this need a upfront 300 ma or time delay rcd?
As its a metal case I have a proper tails gland
Ze=15.25 ohms with a earth fault current of almost 16...
You will only get close to the full rated power when the sun is at 1000 watts per square meter , this assumes no shading, on the back of the panel you should see an open circuit voltage and a short circuit current.