  1. Dabbers

    Why do I have a wall thermostat? is there nothing better?

    I've always gone to the isolation valve and yes I agree wholly with your comment about bonding, my point and biggest gripe is that the gas regs and the electrical regs are not the same. and probably never will be !
  2. Dabbers

    Monitoring by app

    Totally agree with Sparkychick
  3. Dabbers

    Why do I have a wall thermostat? is there nothing better?

    I have had this conversation with so many gas engineers and their answer is that it is no longer referred to a Thermostat its a safety interlock incase the return stat in the boiler fails it can shut down the boiler ????? -------- if you ask me but that is what they need/install to meet their...
  4. Dabbers

    Do I need a 415v coil contactor?

    Most Manufacturers do a single module contactor rated at 20A however they are only 230V coils so you will need a Neutral across A2 and a feed from each switch to A1 let me know if want a drawing..
  5. Dabbers

    UK Static/Tingle from shower/towel rad.

    Gas should be in copper as well as oil.....
  6. Dabbers

    UK Static/Tingle from shower/towel rad.

    I know that you have already checked that the Gas or Oil is bonded?
  7. Dabbers

    UK Static/Tingle from shower/towel rad.

    You say that the shower is fed directly from the boiler so the rads will be as well so they should be at the same potential unless the however the water is plumbed in plastic and the rads in copper for arguments sake so I would check the boiler first for any issues and see if you can ascertain...
  8. Dabbers

    Cable Sizing for Oven...?? Please Help..!!

    Table 4D2A says that a 2.5mm 70 degrees c, cable in a conduit buried in a thermally insulated wall will carry 18.5A 2.5mm cable 70 degrees c, enclosed in conduit or trunking ON a wall will carry 23A with a run of 5 meters VD would not come into it If the cable run with others if so the...
  9. Dabbers

    Live To The Lights Or Switch (Lighting Circuit)

    Me personally i use both methods so for argument sake i would feed the lights in the hall and not the switch because you may well have 2 way up and down plus an external light so you end up with a very busy switch then into the kitchen i may feed the light switch as 3 plating down lights is a...
  10. Dabbers

    DOL starter switch Trips out

    Good Luck! won't be back on till Monday i'll see how you get on then! just another thought is that its worth checking the voltages on the other equipment upstream from the contactor as the voltage would still be low on L1 further up stream
  11. Dabbers

    DOL starter switch Trips out

    Definitely a fault on L1 I would check what James has listed It may well be an isolator or supply cable upstream feeding the DOL that is failing causing a high resistive joint looking at the current readings
  12. Dabbers

    Private rental EICRs are coming soon

    The intention os good, however is drive by dave prepared to be fined or imprisoned for false reporting until that happens they will not be worth the paper that they are written on, only when this happens will people sit up and realize that it is there for their protection not a financial gain...
  13. Dabbers

    DOL starter switch Trips out

    What you might find is the bearings in the motor at starting to seize or the gear box that the motor is driving has become warn out, you could do with a clamp meter on it and if you adjust the overload up you can see the current rise you might find due to its age that another amp makes the motor...
  14. Dabbers

    UK Rcd tripping

    lazy RCD comes to mind I bet since the day it was installed its never been tested do a RCD ramp test and see what current it is tripping out at?
  15. Dabbers

    working at height.

    Personally i would go with your own risk assessment and that should be based upon location, height, access available, time that you need to be up there and personal safety. Good Luck