  1. haptism

    Improver x4 wanted in Holland

    Thought this might be of interest to someone Electrical Improver (Holland) - London - Indeed.co.uk -...
  2. DSCF2007.JPG

    DSCF2007.JPG

  3. DSCF2006.JPG

    DSCF2006.JPG

  4. DSCF2005.JPG

    DSCF2005.JPG

  5. DSCF2004.JPG

    DSCF2004.JPG

  6. haptism

    16mm T&E tails on 100amp fuse

    Checked again today and switch fuse has an 80A. Took some pics of the t&e serving the CU, as you can see theres no glands, no cleats, no rcd to be found. Not sure if theres mechanical protection where the t&e goes into building; what are your thoughts on this. The building was constucted in 2016.
  7. haptism

    16mm T&E tails on 100amp fuse

    Okay, never considered that would be called a submain so that's good info. Will check tomorrow when the house was constructed but im sure it no older than 5 years.
  8. haptism

    16mm T&E tails on 100amp fuse

    But still the tails not rcd'd
  9. haptism

    16mm T&E tails on 100amp fuse

    Yeh I will do tomorrow
  10. haptism

    16mm T&E tails on 100amp fuse

    Its not a sub main, its a semi detached house with its own single phase supply. The switch fuse is there as the tails are longer than 3m, the load side of the switch fuse is t&e which I can only assume is going the the CU. The switch fuse has 100a on it
  11. haptism

    16mm T&E tails on 100amp fuse

    Im not entirely sure as all wiring is back entry into CU, proper tails go from main DNO Fuse to meter and then to switch fuse; from the switch fuse its t&e. So I assume yes it goes to CU
  12. haptism

    16mm T&E tails on 100amp fuse

    Theres definitely no rcd protecting the tails; my issue is I cannot see if the t&e is mechanically protected or not when it goes into building so will note this on the cert also. Is it usual to run tails in t&e on new builds and put in conduit ?? That's a really subjective question. Second...
  13. haptism

    16mm T&E tails on 100amp fuse

    Yes I will be doing that, lesson learnt today, check service head before any works done, not afterwards.
  14. haptism

    16mm T&E tails on 100amp fuse

    Looks like a separate 16mm main earth is run alongside the t&e, I cannot see if the t&e is mechanically protected on way to cu but I doubt it, so yeh, no rcd for that added to the list. I will need to take fuse out of carrier and have a look, maybe its 80A afterall. Yeh PFC looks good, don't...
  15. haptism

    16mm T&E tails on 100amp fuse

    x1 garage socket
  16. haptism

    16mm T&E tails on 100amp fuse

    There is acceptable Ze, main earth at the board is single g/y 16mm, water and gas bonded with 10mm also.
  17. haptism

    16mm T&E tails on 100amp fuse

    Did a job earlier in a new build, part of a 5 year old new build estate in the darkest depths of kent. Anyhow opened up CU and saw 16mm tails so assumed would be on 80a fuse as there not huge demand. Then outside to check service head and main fuse is labelled 100a ?, the tails are 16mm t&e. I...
  18. haptism

    BS 1363 socket circuit

    Its singles in conduit run surface, 6mm singles can then handle 40A. Diversity of the appliances brings the Ib to less than 40A.
  19. haptism

    BS 1363 socket circuit

    Yeah I cant argue with that You what Spin
  20. haptism

    BS 1363 socket circuit

    Yeh could run a ring of 4mm yes. I was more concerned thou about socket circuits with a ocpd of over 32 A as its unorthodox.