This is a picture of the untouched y plan. From the bottom 1,2,3,4 were too the stat so I removed these and linked 1 and 4 together. I know it's hard from Pic but I imagine you experienced engineers will probably see any issue straight away.
This is how it's been for at least a decade
Friend asked me to wire in a hive on a conventional 1 zone heating system. So I fitted it tested the HIVE and all was working.
I then said to him after about 20 minutes your pump is still running even though water and heat were turned off.
Response it's always been like it. So me been fussy...
By moving the the doubled up live to x14 the pump started operating normally. The RT does go to the room stat. As chased it through.
So thanks andyb you are correct.
The installer just missed the x14 because he usually installs worcester but couldn't get one in time.
Thanks for all replies...
So how do I rectify as heating engineer doesn't know. The only boiler connections are live neutral earth and RT.
What is different between this boiler and old boiler. I never saw the connections on the old potterton. Would it of has a pump feed on it?
Hi thanks for reply.
The link has been removed and the heating is working on programmer as you would expect.
The pump is even on if I disconnect the programmer because the L and RT cable in the boiler are fed to connectors behind programmer no to the programmer itself.
Hi
I have just had my boiler replaced which was a potterton suprima 60l. Heat only boiler as it kept cutting out.
I have had a vailent ecofit 425 fitted by engineer but now my pump is running continuously.
This wasn't the case before.
It's s plan with two heating 2 port valves and 1 hot...
Hi thanks for reply.
I was guessing re who installed it. I am not a big fan because its plastic under wooden stairs on only escape route.
It's currently protecting two boards.
Not sure if its acceptable worst case to replace it with stand alone metal spd then come out in to henley blocks to...
Thanks for reply. Dartlec
I have looked at the data sheet and the issue I have is as you say TNCS is not mentioned so is it suitable?
I might contact Wylex directly. To ask the question.
The main fuse I believe is 80amp to to be 100 percent would need to have fuse pulled.
Ok understairs we need metal as we know. We need metal everywhere in domestic properties.
My question relates to a DNO installed plastic isolator with inbuilt spd under stairs next to my nice new metal consumer unit.
Are they allowed. If its deemed dno equipment then I know they have different...
Having an issue with 2919 edition 4 book. Should have been delivered as promised today but now tomorrow which is not great as course tomorrow.
I know should of had earlier.
Does anyone have a copy any where near birmingham, lichfield derby areas that I can either buy beg borrow or steal...
How would you like to explain it so we can avoid the endless circle.
I was referring to an article in electri
https://professional-electrician.com/technical/stroma-certification-supply-chain/
Doesn't say it's not allowed but was referring back to this.
Was having bad day yesterday. Little.one went to hospital with peanut reaction so will take it o the chin.
Mr TJAnderson has opened my eyes to looking at it from a different perspective and he is entirely correct in his xlpe comment on cable selection.
I have got another very experienced...