  1. D

    Earthing & electrical suppliers

    Evening.. So, I'm working on a house that has been split into 2 flats and have been asked to do a board change in the downstairs flat. The earthing arrangement is TNS but I noticed that there is an earth connected between the neutral of the cut out and the earth terminal block to create a PME...
  2. D

    Live cable taken straight off busbar..Reg no. required.

    There is a cover for the busbars, it was just loosely placed over as the offending cable prevents it being screwed down. I would have to notch out the cover to fix it down.
  3. D

    Live cable taken straight off busbar..Reg no. required.

    I didn't have my pinhole camera with me that day to take a picture with the cover on, so had to take the cover off for the picture! It was only off for seconds..promise.
  4. D

    Live cable taken straight off busbar..Reg no. required.

    Ok..that's the answer I was looking for then!!! Cheers
  5. D

    Live cable taken straight off busbar..Reg no. required.

    It's not the fact that it is feeding a switched fuse, that is right next to the db, it's the fact that a cable has been crimped on to a busbar that bothers me, so asked for clarification.
  6. D

    Live cable taken straight off busbar..Reg no. required.

    The next part of my question should have been 'if any regs at all'. It just doesn't seem right, those nuts/bolts are to fix the busbars in place, not for additional cables to fix to.
  7. D

    Live cable taken straight off busbar..Reg no. required.

    Evening...Can anyone tell me which reg this breaks?? It feeds a switched fuse.
  8. 20171025_104155.jpg

    20171025_104155.jpg

  9. D

    Vistalux mcb equivalent

    They sell them on ebay, but I need an equivalent to get me through tomorrow.
  10. D

    Vistalux mcb equivalent

    Evening all...just wondering if anyone knows of an equivalent mcb to the obsolete Vistalux AUB 1 range?? Cheers
  11. D

    EICR pricing advice.

    Going in blind...nothing available..probably never been tested since install which I reckon was about 30 years ago.
  12. D

    EICR pricing advice.

    Periodic is an answer..it's the answer I gave
  13. D

    EICR pricing advice.

    A periodic Periodic..
  14. D

    EICR pricing advice.

    I have been asked to do an EICR for a community centre, there are 9 consumer units throughout the building..just after a bit of advice on how you would go about pricing a job like this?
  15. D

    Method to install 19.6KW oven in single phase property

    I didn't state, as what's there already is irrelevant to the question I was asking.
  16. D

    Method to install 19.6KW oven in single phase property

    It all sounds a bit 'stick a 50amp breaker in and hope it doesn't trip out on crimbo day'! My first thought was to do this but was just wondering if there were any other ideas about how to do it..all the specs and calcs tell you it should pull over 50 amps.
  17. D

    Method to install 19.6KW oven in single phase property

    Cooker TR93IBL - Smeg - http://www.smeguk.com/product/tr93ibl/
  18. D

    Method to install 19.6KW oven in single phase property

    As the title says, a customer has bought a 19.6 Kw 3 oven/6 induction hob burner that they have kindly asked me to install for them into their 3 bedroom semi! I'm a bit stuck as to go about this as the amps it pulls is over 80, I know there will be some diversity etc but has anyone any...
  19. D

    Extractor fans in kitchens, bathrooms and utility rooms.

    Morning.. Just wondering if anyone knows what official building regs state about having to install the above when doing a refurb of house? I have had building control officers tell me in the past that fans are required in kitchens bathrooms and utility rooms, but I can't find anything in the...
  20. D

    Adding meter to 3 phase supply

    There is a 3 phase supply coming into the building. Phase 1 goes through a single phase meter then up to the flat cu via 100a isolator. Phase 2 goes through another single phase meter to the existing shop cu. Phase 3 is spare. I am just designing the installation so no measurementsuch have...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top