I am afraid what you have here is a bodge! Someone has run out of cores and used the earth (g/y) as a switch wire. Earths appear to have been dispensed with. Although I could tell you which wires to connect together, I suggest you get a local spark to pop in and check the install to ensure it’s...
If you look at the attached curves, you will see that a 5A fuse will run at 8A for a considerable time before blowing, but the fuse will be getting very hot which is probably what caused the insulation to melt in the plug top.
People think that if you stick a fuse in it will blow as soon as it...
I had this conversation with an HSE inspector a number of years ago.
Basically, if you work live and something goes wrong and an injury to you or someone else happens as a result, you had better have a good reason for working live. The reason for working live has to outweigh the risk of not...
Also need to consider that the motor should be IE3 compliant, doubt the Chinese have heard of that either!
One other thing to note is the fault level from the converter may be insufficient to operate over current devices in the prescribed time in the event of an over current fault. Maybe worth...
I think you need to get one of the regular users of the system to input their code, set the system, then get them to unset the system.
It should then be out of engineer mode.
It’s impossible to say from your description on how this has been wired or what the mystery wiring is that are passing through.
I would suggest you get a spark to look at this and you never know he may be able to pull a neutral down to the switch in the bedroom too!