EICRs are open to so much interpretation it’s actually ridiculous.
Let me put it this way. There’s no way I’d be able to confidently hand over an EICR without verifying the type, condition and connection of electrode. End of the day, like said above, it’s down to the assessor. You make your...
Let me start by saying I read a lot of your posts Essex and I know you know your ---- & respect your opinions.
However, I can’t back this pal I just can’t.
1) You have no clue what you’re testing, or how many.
2) external conditions could influence the decent readings when in reality you...
You have 2 questions, I have 1:
Why do you automatically presume Rod?
What’s to say you haven’t got an earth plate electrode?
Anyway, let’s presume Rod. You have no idea whether:
A) the rod is of suitable material & size despite the decent reading.
B) whether it’s correctly installed via a...
Lol.
“Signing off electrical work”
You’re a plumber not a spark stick to your own trade. Part-P isn’t a qualification it’s a building reg.
This thread is ridiculous.
I feel like an apprentice again, or worse a Electrical Trainee.
I’d grade it with a squiggle that cant be deciphered - I’ll make it look like a 1,2,3 and a tick, maybe even a N/A to cover all basis.
I’m off to bed. If I dream about spurs, I hate you all.
Oh no let’s not start this again!
None of us with a brain cell would ever do it this way anyway, so even if it isn’t against the regs let’s just pretend it is?
Someone said they’d only ever do it like this if they absolutley had too - but I can’t even imagine a scenario which would make this...
OP. Basically fella, you’ve opened a can of worms.
After reading this, and seeing SparkyChick taking on the forum. My opinion is: What you’ve done is bad practice and I would never ever do it like this, and I’ve always been taught that this is wrong. But - hey, it doesn’t appear to be against...
1) Do not pay a penny, that’s a disgrace.
2) If the Cowboy gets argumentative report him to trading standards for doing work well out of his capabilities. Also, link him to this thread on this forum and inpaticular the paragraph below
STOP! You absolute <insert word> You’re completely out of...
I apologise for my language this morning and my post was correctly edited by a mod. My outburst was probably a little OTT and if I came across as rude it wasn’t my intention, just this sort of stuff does boil the p155 of electricians.
Maybe I should of read more, but I still think what you...
I’ve read the first 3 pages of this thread only.
And I am absolutely baffled that nobody has called the OP out for being out of his depth.
I’m all for DIY ... if I wasn’t I’d be a hypocrite as I change car tyres on my vehicles. But DIY is absolutley not splitting rings and wiring fresh whether...
I like to wrap my CPC in Brown, especially when installing new lighting circuits.
This way when Mr.DIY changes his light fittings, and doesn’t have a clue what he’s doing, he has no eyebrows left.
P.S Jk.
True, but anyone with an ounce of common sense would arrange for the electrics to be relocated prior to the garage door being installed.
Client just as much at fault.
P.S I have absolutley no idea why I’ve just given a kiss on the above post haha. I won’t edit though, have the kiss, enjoy the kiss, embrace the kiss ... you won’t be getting anymore haha
Conduit makes the job more professional & also, it’s easier to re-route cables when the architect suddenly decides it’s Monday morning and he’s going to change the drawings for the 100th time.