What I am working up as a solution is a very fast ac changeover switch to connect the ac output socket to either the inverter or the incoming grid mains but never both. Would you be happy with the changeover which happens within a few cycles of the ac mains so should not be noticeable?
I will do the same measurements on one of my brother in law’s solar leccy vans and see what I measure. Don’t think it is a problem but best to be sure.
Davesparks idea does keep things nice and simple which is always a good thing for reliability and low cost.
My brother in law’s catering vans use gas for all heating of water, fryers, grills and hob and solar leccy, batteries with genie back up for the freezers, chillers, refrigeration and...
What is your budget for the provision of mains power in the van? To the nearest £500, ie £1000 or £3500 or £10000.
How many years do you expect to operate the mobile coffee business?
How many days per week and weeks per year do you reckon the business will trade?
I am wondering if the best...
Very helpful information which casts much light on the problem. It says an up-front rcd is 'not recommended' - rather weak language methinks. It either is or is not required. Anyway, with more mental energy than last time I have the outline of a solution. But before I desrcibe it and also...
If you do this job then a series of time-lapse images from start to finish would be nice to watch. And a few remarks and comments by each perhaps in way of a master-class.
I will mull over what have sent me which will make my rail journey North next week pass quickly. I was cooking a three course meal for 50 last night in our church social club so am a bit weary today for any serious thinking. But a quick question now - is the dedicated consumer unit for off...
Tonyboy: I had a reply from Voltacon Conventry but it did not address my clarification with rigour so I have sent a further missive to them. Helpfully, they said they would study the wiring in of the cabinet so I have sent them your sketch with some additional bits by me and a drawing of how...
Tonyboy: I have sent this to Voltacon:
To: [email protected];
17/02/2023 06:43
1
Silent Power SP5048-C-P, PLUG 'N' PLAY PHOTOVOLTAIC CONTROL CABINET Off Grid Inverter Charger Kit 5000Watt -
https://voltaconsolar.com/silent-power-sp5048-c-p.html
Dear Sir or Madam,
May I clarify...
By way of clarification, that box marked Cronos Voltage is measuring the input voltage between L and N and checking it is within range ie say 230V +/- 10V, and if it is it then closes a contact which then applies power to the contactor next to it to supply power to the input of the inverter. If...
Just to be sure - nothing you have done wrong - but would you measure the resistance between the two blue N connections at the bottom of the inverter box - see attached image and area circled in blue. If there are ac isolator switches on the the inverter box then please turn these on. As...
Thank you for the readings at B and C which indicate that N and E are connected together at the output side of the inverter to create a TN-S earthing system. (Just to confirm I assume you are on the lowest Ohms range and 00.2 is 00.2 Ohms ie less than 1 Ohm. To be sure what reading do you get...
What literature do you have that you can send me or a link to? Do you have a circuit diagram for the cabinet?
If your cabinet has on one side as in the earlier video clip two c forms for mains in and inverter out then I can spell out a way to do the measurements at the socket or plug N and E...