I am confused about section on page 6 * Employee repersntative are.... I am only one in my company.
also * Consultaion with emploees is provided by ,.........
Hi Guy. Could any one please help me with company letter head template. I have my first NICEIC assessment this week and assessor want to see some paper work prior to assessment. Company letter head is one of them. He also want see signed H&E policy( he wouldn't accept what I sent to him)...
Thanks a lot! My mft did show this value but I did not note it so I will leave it blank at the moment but will note it next time. I am also struggling upload my tester detail, It shows in admin section but not in "circuits and test result" page. Thanks
There are some ceiling fans(with light combined) in the circuits.It will be difficult to disconnect them. Is it okay to swich them off when doing IR? or just leave LIM blank as previously suggested? Thanks
Thanks for your valueable comments. In my humble opinion this is not new installation.I changed the consumer unit and installed a new circuit for smoke alarm .I mentioned this under
"Extent of the installation covered by this Certificate". Please correct me if I am wrong here.Thanks again.
I had an email from assessor to email him IEC. Please advise if it is good enough to emailed to him. Could you please information why insulation reader is lesser when testing between Live-Earth than live- live?Thanks
Thanks a lot! Some how if I Test insulation between live L to N , L to E or N to E it goes over 150 mega ohm but extremely low when tested between LIVE-LIVE joine togather to E. Don't know why.Thanks again
Thanks a lot! Wiring is of new coloursbut abot 10-15 years old. I will test these lighting circuit again with lamps removed. You are right about cpc link as there is 2 gang stair light switch (Two way),Is there a way to avoid this? Zs at DB also 0.21 as you correctly pointed out! about class ll...
I managed to test and fill a certificate, which I going to upload. Guys please have a look and advise me if you find some mistakes. The consumer board has a SPD pre installed which I don't know how to test. I will use Elecraformin the end as this is temporary. Thanks in advance.
Bought a software from ebay with different colours (black,blue, green and purple)certificates and digital version of reg books.I also have hard copy of Regs book. Are these okay to use for time being until I get registerd with NICEIC ?Thanks