  1. N

    UK IP 65/IP44

    Thanks for the information much appreciated
  2. N

    UK IP 65/IP44

    A 10Way TPN MCCB Distribution Board is qùite large ….. would be difficult to put in an enclosure….however I have seen the gear tray /pan removed from a distribution board & fitted in a stainless steel enclosure in a food manufacturing process area. Not sure if that complies with BS 7671 though???
  3. N

    UK IP 65/IP44

    The existing switchgear is to BS 5419 with some of the switches containing asbestos arc shields, also some of the SWA cables are not correctly glanded of properly. Some have BS 88 fuses others BS3036. Also in the event of a fault all three poles won’t be disconnected.
  4. N

    UK IP 65/IP44

    Yes BS 5419 must of had a blonde moment when I put the other BS number. The switch room is built adjacent to a production area where swa cables pass through a wall into the switch room . Would you seal all holes first that monitor the switch room for ingress of dust for a few days …. Then if...
  5. N

    UK IP 65/IP44

    Even thought about putting some fans in room to make the room under positive pressure to stop any ingress
  6. N

    UK IP 65/IP44

    James thanks firstly for the response. Yes the switch room can be sealed off better as several swa cables enter from the production area into the switch room . I’ve just started working there then they tell me they need to satisfy All C2 on the report for their insurance. I’ve managed to source...
  7. N

    UK IP 65/IP44

    Main switch room as ingress of dust , the switch room also has many openings to allow the ingress of dust. A recent EICR as coded the Distribution equipment in the room C2 not fit for external influences . One side of the room as an 800A BS 5709 isolator supplying a busbar with 10 BS 5709...