  1. newbie24

    Set up for oven + combi?

    Manual for combi says that, the oven one doesn't specify. I think I'm just going to get 2 new supplies at 16amps each on 2.5mm t&e. Feels like more bulletproof approach. Could put the oven on a 20 but 16 would cover 3.49kw
  2. newbie24

    Set up for oven + combi?

    Thanks, I think that's the route I'm going down. Presumably the load ratings for the combi is oven+grill+microwave, so in reality it's going to be a lot lower than the 3kw rating, and for oven it will be oven+grill, so again you are only going to be running part of 3.5kw. It's a much higher...
  3. newbie24

    Set up for oven + combi?

    Thanks, I did consider that as an option. Do FCUs always have the 3mm separation required? The manual for the combi says a fuse between 15 and 20amps, if I did downgrade the MCB so you think I'd get nuisance tripping or would it likely be ok?
  4. newbie24

    Set up for oven + combi?

    Been having a discussion with my electrician on the best way to wire up a new oven and a combi oven/microwave and would appreciate some more input. There is an existing cooker connection in 10mm t&e with a 32a MCB (and RCD protection). The oven is 3.49kw and the combi is 3kw. Oven doesn't have...